Thermostat is included, associated with boiler receiver unit. When I change value on the thermostat directly, controller sees the changes in Thermostat Control device, but when I change Thermostat Control device value, thermostat doesn't see it. Or see after some time, like 20 or 30 mins. Any ideas why is this happening?
Last edited by IgoriokLT on 17 Sep 2019 01:35, edited 1 time in total.
User avatar
PoltoS
Posts: 7565
Joined: 26 Jan 2011 19:36

Re: SRT321 Thermostat doens't accept controller Set value.

Post by PoltoS »

Do you see the Thermostat Set packet in the queue? I suppose it is pending in the queue until the device wakes up
IgoriokLT
Posts: 87
Joined: 09 Oct 2016 15:24

Re: SRT321 Thermostat doens't accept controller Set value.

Post by IgoriokLT »

Yeah, sorted this out. Changed wake-up time to 240, I forgot this is not FLiRS device.