Danfoss LC - No wakeup comm with 1.4.1rc1

Posted: 19 Nov 2013 13:29
by JV
Seems the DLC only communicates with Razberry when I press the middle button on the device itself.

Razberry Z-Wave Job queue shows these messages forever:

ThermostatSetPoint Set
ThermostatSetPoint Get

They keep in queue forever, until I press the button on the device.

I excluded the device and then re-included, which both worked fine. No change. I updated the routes, they are green.

It worked fine before 1.4, and 1.4.1rc1 did not seem to solve the problem.

Am I the only one with this problem?

Solved - Included but no M for mounted

Posted: 19 Nov 2013 13:29
by JV
Although I reincluded, it had not completely mounted (flashing M in display). After I did this, it seems to work fine and I now see communication every 5 minutes.