I have problems with Heatit Z-TRM3 thermostat dropping out from Z-Wave network. I've had older Heatit Thermostat for years without any problems, and recently bought two newer Z-TRM3 thermostats, and problems started immediately with both of them.
Once up and running, either one of the new Z-TRMs drops out after some time (never the old one), sometimes it happens after one day, sometimes they may last a week or two, but I can't recall they would have lasted even a month. Something to note is that I haven't seen them both dropping at the same time, just as if they would act better alone, ie as if they would interfere each other (not sure if this is possible, at least it shouldn't).
In Z-way, device is reported as "dead", and only way to bring it back is to switch off mains power and then switch back on, then it is back online for a while until it happens again for either of them.
For the setup, I have z-way with latest firmware running in Raspberry Pi3. There are 15 devices in the network, and these thermostats are within few meters from the z-way controller, included with S0. I've tried network reorganization, but did not seem to matter.
Any ideas what's wrong? Since I have two units acting the same, I doubt it's either of my Z-TRM3s that is broken. And since there are no reports from other users, it's also hard to believe Z-TRM3 in general would act in a wrong way, so perhaps something in z-way that cannot handle (it seems there is confusion about the nonce reports)?
Attached are logs (I handpicked the parts that seem relevant to me, please let me know if I should post more from some timeframe), in the logs the failing thermostat is with ID 23.
Have to note also that these devices produce a lot of z-wave traffic, values are reported very often, every few seconds.
[2021-06-29 16:11:30.778] [D] [zway] SETDATA devices.23.data.lastReceived = 0 (0x00000000)
[2021-06-29 16:11:30.798] [I] [zway] Node 23:0 CC Security: sending Nonce Report
[2021-06-29 16:11:30.798] [I] [zway] Adding job: Nonce Report
[2021-06-29 16:11:30.799] [D] [zway] RECEIVED: ( 01 0C 00 04 00 17 02 98 40 C9 00 01 03 F1 )
[2021-06-29 16:11:30.799] [D] [zway] SENT ACK
[2021-06-29 16:11:30.799] [D] [zway] SETDATA devices.23.data.lastReceived = 0 (0x00000000)
[2021-06-29 16:11:30.868] [I] [zway] Node 23:0 CC Security: sending Nonce Report
[2021-06-29 16:11:30.868] [I] [zway] Adding job: Nonce Report
[2021-06-29 16:11:30.868] [D] [zway] RECEIVED: ( 01 0C 00 04 00 17 02 98 40 CA 00 01 03 F2 )
[2021-06-29 16:11:30.868] [D] [zway] SENT ACK
[2021-06-29 16:11:30.868] [D] [zway] SETDATA devices.23.data.lastReceived = 0 (0x00000000)
[2021-06-29 16:11:30.919] [I] [zway] Node 23:0 CC Security: sending Nonce Report
[2021-06-29 16:11:30.919] [I] [zway] Adding job: Nonce Report
[2021-06-29 16:11:37.099] [I] [zway] Job 0x13 (Nonce Report): Job not sent before timeout
[2021-06-29 16:11:37.099] [I] [zway] Job 0x13 (Nonce Report): Cancelling job: Nonce Report
[2021-06-29 16:11:37.099] [I] [zway] Removing job: Nonce Report
[2021-06-29 16:11:37.130] [I] [zway] Job 0x13 (Nonce Report): Job not sent before timeout
[2021-06-29 16:11:37.130] [I] [zway] Job 0x13 (Nonce Report): Cancelling job: Nonce Report
[2021-06-29 16:11:37.130] [I] [zway] Removing job: Nonce Report
[2021-06-29 16:11:37.447] [I] [zway] Job 0x13 (Nonce Report): Job not sent before timeout
[2021-06-29 16:11:37.447] [I] [zway] Job 0x13 (Nonce Report): Cancelling job: Nonce Report
[2021-06-29 16:11:37.447] [I] [zway] Removing job: Nonce Report
[2021-06-29 16:11:37.519] [I] [zway] Job 0x13 (Nonce Report): Job not sent before timeout
[2021-06-29 16:11:37.519] [I] [zway] Job 0x13 (Nonce Report): Cancelling job: Nonce Report
[2021-06-29 16:11:37.519] [I] [zway] Removing job: Nonce Report
[2021-06-29 16:11:37.549] [I] [zway] Job 0x13 (Nonce Report): Job not sent before timeout
[2021-06-29 16:11:37.550] [I] [zway] Job 0x13 (Nonce Report): Cancelling job: Nonce Report
[2021-06-29 16:11:37.550] [I] [zway] Removing job: Nonce Report
[2021-06-29 16:11:37.631] [I] [zway] Job 0x13 (Nonce Report): Job not sent before timeout
[2021-06-29 16:11:37.631] [I] [zway] Job 0x13 (Nonce Report): Cancelling job: Nonce Report
[2021-06-29 16:11:37.631] [I] [zway] Removing job: Nonce Report
[2021-06-29 16:11:37.713] [I] [zway] Job 0x13 (Nonce Report): Job not sent before timeout
[2021-06-29 16:11:37.713] [I] [zway] Job 0x13 (Nonce Report): Cancelling job: Nonce Report
[2021-06-29 16:11:37.713] [I] [zway] Removing job: Nonce Report
[2021-06-29 16:11:37.805] [I] [zway] Job 0x13 (Nonce Report): Job not sent before timeout
[2021-06-29 16:11:37.805] [I] [zway] Job 0x13 (Nonce Report): Cancelling job: Nonce Report
[2021-06-29 16:11:37.805] [I] [zway] Removing job: Nonce Report
[2021-06-29 16:11:38.184] [I] [zway] Job 0x13 (Nonce Report): Job not sent before timeout
[2021-06-29 16:11:38.184] [I] [zway] Job 0x13 (Nonce Report): Cancelling job: Nonce Report
[2021-06-29 16:11:38.186] [I] [zway] Removing job: Nonce Report
[2021-06-29 16:11:38.605] [D] [zway] RECEIVED: ( 01 18 00 13 EA 01 03 14 00 7F 7F 7F 7F 7F 01 01 07 00 00 00 00 02 15 10 14 63 )
[2021-06-29 16:11:38.605] [D] [zway] SENT ACK
[2021-06-29 16:11:38.605] [I] [zway] Job 0x13 (Nonce Report): Not delivered to recipient
[2021-06-29 16:11:38.606] [I] [zway] Node 18:0 CC Security: sending Nonce Get
[2021-06-29 16:11:38.613] [D] [zway] Delivered to Z-Wave stack
[2021-06-29 16:11:38.891] [I] [zway] Job 0x13 (Nonce Report): Job not sent before timeout
[2021-06-29 16:11:38.892] [I] [zway] Job 0x13 (Nonce Report): Cancelling job: Nonce Report
[2021-06-29 16:11:38.892] [I] [zway] Removing job: Nonce Report
[2021-06-29 16:11:38.912] [I] [zway] Job 0x13 (Nonce Report): Job not sent before timeout
[2021-06-29 16:11:38.912] [I] [zway] Job 0x13 (Nonce Report): Cancelling job: Nonce Report
[2021-06-29 16:11:38.912] [I] [zway] Removing job: Nonce Report
[2021-06-29 16:11:38.984] [I] [zway] Job 0x13 (Nonce Report): Job not sent before timeout
[2021-06-29 16:11:38.984] [I] [zway] Job 0x13 (Nonce Report): Cancelling job: Nonce Report
[2021-06-29 16:11:38.984] [I] [zway] Removing job: Nonce Report
[2021-06-29 16:11:45.785] [D] [zway] Job 0x13: deleted from queue
[2021-06-29 16:11:46.437] [D] [zway] RECEIVED: ( 01 18 00 13 EB 01 03 0D 00 7F 7F 7F 7F 7F 01 01 07 00 00 00 00 02 12 02 17 6D )
[2021-06-29 16:11:46.437] [D] [zway] SENT ACK
[2021-06-29 16:11:46.437] [I] [zway] Job 0x13 (Nonce Report): Not delivered to recipient
[2021-06-29 16:11:46.438] [D] [zway] SENDING (cb 0xec): ( 01 11 00 13 17 0A 98 80 E9 70 C3 12 5D 5C 6B 29 25 EC 3A )
[2021-06-29 16:11:46.440] [D] [zway] RECEIVED ACK
[2021-06-29 16:11:46.446] [D] [zway] RECEIVED: ( 01 04 01 13 01 E8 )
[2021-06-29 16:11:46.446] [D] [zway] SENT ACK
[2021-06-29 16:11:46.447] [D] [zway] Delivered to Z-Wave stack
[2021-06-29 16:11:53.395] [D] [zway] SENT ACK
[2021-06-29 16:11:53.395] [I] [zway] Job 0x13 (Nonce Report): Not delivered to recipient
[2021-06-29 16:11:53.396] [I] [zway] Job 0x13 (Nonce Report): Removing job due to too much retransmitions
[2021-06-29 16:11:53.396] [I] [zway] Adding job: Check if node is failed
[2021-06-29 16:11:53.396] [D] [zway] Job 0x13 (Nonce Report): fail
[2021-06-29 16:11:53.396] [I] [zway] Removing job: Nonce Report
[2021-06-29 16:11:53.396] [D] [zway] SENDING: ( 01 04 00 62 17 8E )
[2021-06-29 16:11:53.397] [D] [zway] RECEIVED ACK
[2021-06-29 16:11:53.401] [D] [zway] RECEIVED: ( 01 04 01 62 01 99 )
[2021-06-29 16:11:53.401] [D] [zway] SENT ACK
[2021-06-29 16:11:53.401] [D] [zway] SETDATA devices.23.data.isFailed = True
[2021-06-29 16:11:53.402] [I] [zway] Job 0x62 (Check if node is failed): Node 23 is failed
[2021-06-29 16:11:53.402] [D] [zway] Job 0x62 (Check if node is failed): success
[2021-06-29 16:11:53.402] [D] [zway] SETDATA devices.23.data.failureCount = 1 (0x00000001)
[2021-06-29 16:11:53.402] [D] [zway] SETDATA devices.23.data.lastSendInternal = **********
[2021-06-29 16:11:53.402] [I] [zway] Removing job: Check if node is failed
[2021-06-29 16:11:53.402] [D] [zway] SENDING (cb 0xed): ( 01 11 00 13 16 0A 98 80 C1 54 A7 C4 3E E4 17 28 25 ED 22 )
[2021-06-29 16:11:53.407] [D] [zway] RECEIVED ACK
[2021-06-29 16:11:53.409] [D] [zway] RECEIVED: ( 01 04 01 13 01 E8 )
[2021-06-29 16:11:53.409] [D] [zway] SENT ACK
[2021-06-29 16:11:53.409] [D] [zway] Delivered to Z-Wave stack
[2021-06-29 16:11:53.437] [D] [zway] RECEIVED: ( 01 18 00 13 ED 00 00 02 00 C9 7F 7F 7F 7F 00 00 03 00 00 00 00 03 01 00 00 D3 )
[2021-06-29 16:20:00.617] [I] [zway] Node 23:0 CC Security: sending Nonce Get
[2021-06-29 16:20:00.617] [D] [zway] SETDATA devices.23.instances.0.commandClasses.152.data.rNonceAckWait = **********
[2021-06-29 16:20:00.617] [I] [zway] Adding job: Nonce Get
[2021-06-29 16:20:00.617] [D] [zway] SETDATA devices.23.data.lastNonceGet = 109167972 (0x0681c564)
[2021-06-29 16:20:00.617] [D] [zway] SENDING (cb 0x26): ( 01 0A 00 13 0F 03 32 01 10 25 26 CA )
[2021-06-29 16:20:00.623] [W] [zway] Received SOF, while awaiting ACK
[2021-06-29 16:20:00.627] [D] [zway] RECEIVED: ( 01 0F 00 04 00 05 06 31 05 04 22 00 00 BE 00 00 5B )
[2021-06-29 16:20:00.627] [D] [zway] SENT ACK
[2021-06-29 16:20:30.527] [D] [zway] RECEIVED: ( 01 18 00 13 34 01 02 C7 00 7F 7F 7F 7F 7F 01 01 07 00 00 00 00 02 11 10 17 68 )
[2021-06-29 16:20:30.528] [D] [zway] SENT ACK
[2021-06-29 16:20:30.528] [I] [zway] Job 0x13 (Nonce Get): Not delivered to recipient
[2021-06-29 16:20:30.529] [I] [zway] Job 0x13 (Nonce Get): Removing job due to too much retransmitions
[2021-06-29 16:20:30.529] [D] [zway] SETDATA devices.23.data.failureCount = 2 (0x00000002)
[2021-06-29 16:20:30.529] [D] [zway] SETDATA devices.23.data.lastSendInternal = **********
[2021-06-29 16:20:30.529] [D] [zway] Job 0x13 (Nonce Get): fail
[2021-06-29 16:20:30.529] [I] [zway] Node 23:0 CC Security: sending Nonce Get
[2021-06-29 16:20:30.529] [D] [zway] SETDATA devices.23.instances.0.commandClasses.152.data.rNonceAckWait = **********
[2021-06-29 16:20:56.015] [I] [zway] Adding job: Nonce Report
[2021-06-29 16:20:56.015] [D] [zway] Job 0x13: deleted from queue
[2021-06-29 16:20:56.026] [D] [zway] Job 0x13: deleted from queue
[2021-06-29 16:20:56.218] [D] [zway] Job 0x13: deleted from queue
[2021-06-29 16:21:02.365] [D] [zway] RECEIVED: ( 01 18 00 13 43 01 02 E2 00 7F 7F 7F 7F 7F 01 01 07 00 00 00 00 02 13 16 17 3E )
[2021-06-29 16:21:02.366] [D] [zway] SENT ACK
[2021-06-29 16:21:02.366] [I] [zway] Job 0x13 (Nonce Get): Not delivered to recipient
[2021-06-29 16:21:02.366] [I] [zway] Job 0x13 (Nonce Get): Removing job due to too much retransmitions
[2021-06-29 16:21:02.367] [D] [zway] SETDATA devices.23.data.failureCount = 3 (0x00000003)
[2021-06-29 16:21:02.367] [D] [zway] SETDATA devices.23.data.lastSendInternal = **********
[2021-06-29 16:21:02.367] [D] [zway] Job 0x13 (Nonce Get): fail
[2021-06-29 16:21:02.367] [I] [zway] Node 23:0 CC Security: sending Nonce Get
[2021-06-29 16:21:02.367] [D] [zway] SETDATA devices.23.instances.0.commandClasses.152.data.rNonceAckWait = **********
[2021-06-29 16:21:02.367] [I] [zway] Adding job: Nonce Get
[2021-06-29 16:21:02.367] [I] [zway] Removing job: Nonce Get
[2021-06-29 16:22:12.814] [D] [zway] Job 0x3b: deleted from queue
[2021-06-29 16:22:17.819] [D] [zway] RECEIVED: ( 01 18 00 13 4D 01 02 DC 00 7F 7F 7F 7F 7F 01 01 07 00 00 00 00 02 11 10 17 0A )
[2021-06-29 16:22:17.819] [D] [zway] SENT ACK
[2021-06-29 16:22:17.819] [I] [zway] Job 0x13 (Nonce Get): Not delivered to recipient
[2021-06-29 16:22:17.820] [D] [zway] SENDING (cb 0x4e): ( 01 09 00 13 17 02 98 40 25 4E 43 )
[2021-06-29 16:22:17.821] [D] [zway] RECEIVED ACK
[2021-06-29 16:22:17.827] [D] [zway] RECEIVED: ( 01 04 01 13 01 E8 )
[2021-06-29 16:22:17.827] [D] [zway] SENT ACK
[2021-06-29 16:22:17.827] [D] [zway] Delivered to Z-Wave stack
[2021-06-29 16:22:20.836] [D] [zway] RECEIVED: ( 01 0B 00 04 00 16 02 98 40 CA 00 00 F6 )
[2021-06-29 16:22:20.836] [D] [zway] SENT ACK
[2021-06-29 16:22:20.837] [D] [zway] SETDATA devices.22.data.lastReceived = 0 (0x00000000)
[2021-06-29 16:22:20.840] [I] [zway] Node 22:0 CC Security: sending Nonce Report
[2021-06-29 16:22:20.841] [I] [zway] Adding job: Nonce Report
[2021-06-29 16:22:22.554] [I] [zway] Adding job: Get background noise level
[2021-06-29 16:22:25.178] [D] [zway] RECEIVED: ( 01 18 00 13 4E 01 02 DF 00 7F 7F 7F 7F 7F 01 01 07 00 00 00 00 02 11 10 14 09 )
[2021-06-29 16:22:25.178] [D] [zway] SENT ACK
[2021-06-29 16:22:25.178] [I] [zway] Job 0x13 (Nonce Get): Not delivered to recipient
[2021-06-29 16:22:25.178] [I] [zway] Job 0x13 (Nonce Get): Removing job due to too much retransmitions
[2021-06-29 16:22:25.179] [D] [zway] SETDATA devices.23.data.failureCount = 4 (0x00000004)
[2021-06-29 16:22:25.179] [D] [zway] SETDATA devices.23.data.lastSendInternal = **********
[2021-06-29 16:22:25.179] [D] [zway] Job 0x13 (Nonce Get): fail
[2021-06-29 16:22:25.179] [I] [zway] Node 23:0 CC Security: sending Nonce Get
[2021-06-29 16:22:25.179] [D] [zway] SETDATA devices.23.instances.0.commandClasses.152.data.rNonceAckWait = **********
[2021-06-29 16:22:25.179] [I] [zway] Adding job: Nonce Get
[2021-06-29 16:22:25.179] [I] [zway] Removing job: Nonce Get
[2021-06-29 17:23:42.099] [D] [zway] RECEIVED: ( 01 18 00 13 3F 01 02 F1 00 7F 7F 7F 7F 7F 00 01 07 00 00 00 00 02 11 10 17 54 )
[2021-06-29 17:23:42.100] [D] [zway] SENT ACK
[2021-06-29 17:23:42.100] [I] [zway] Job 0x13 (Nonce Get): Not delivered to recipient
[2021-06-29 17:23:42.100] [D] [zway] SENDING (cb 0x40): ( 01 09 00 13 17 02 98 40 25 40 4D )
[2021-06-29 17:23:42.102] [D] [zway] RECEIVED ACK
[2021-06-29 17:23:42.108] [D] [zway] RECEIVED: ( 01 04 01 13 01 E8 )
[2021-06-29 17:23:42.108] [D] [zway] SENT ACK
[2021-06-29 17:23:42.108] [D] [zway] Delivered to Z-Wave stack
[2021-06-29 17:23:43.279] [D] [zway] Job 0x3b: deleted from queue
[2021-06-29 17:23:45.120] [D] [zway] Job 0x13: deleted from queue
[2021-06-29 17:23:45.222] [D] [zway] Job 0x13: deleted from queue
[2021-06-29 17:23:45.334] [D] [zway] Job 0x13: deleted from queue
[2021-06-29 17:23:49.146] [D] [zway] RECEIVED: ( 01 18 00 13 40 01 02 BF 00 7F 7F 7F 7F 7F 01 01 07 00 00 00 00 02 11 10 17 64 )
[2021-06-29 17:23:49.147] [D] [zway] SENT ACK
[2021-06-29 17:23:49.147] [I] [zway] Job 0x13 (Nonce Get): Not delivered to recipient
[2021-06-29 17:23:49.147] [I] [zway] Job 0x13 (Nonce Get): Removing job due to too much retransmitions
[2021-06-29 17:23:49.147] [D] [zway] SETDATA devices.23.data.failureCount = 5 (0x00000005)
[2021-06-29 17:23:49.147] [D] [zway] SETDATA devices.23.data.lastSendInternal = **********
[2021-06-29 17:23:49.147] [D] [zway] Job 0x13 (Nonce Get): fail
[2021-06-29 17:23:49.147] [I] [zway] Node 23:0 CC Security: sending Nonce Get
[2021-06-29 17:23:49.147] [D] [zway] SETDATA devices.23.instances.0.commandClasses.152.data.rNonceAckWait = **********
Re: Problems with Heatit Z-TRM3 dropping
It might be that both hangs at nearly same moment. More interesting would be to see the log during the moment they hang - may be they don't like some command and hang. Try to ask HeatIt - may be they know the issue.
Also make sure to upgrade the firmware to the latest!
samuli_jarvela
Like I said, they never hang at the same time. The given logs show the moment one of them hanged, and like I said there are lots of errors with nonce reports, anything wrong with them? Also, like I said, once the other one hangs, the other keeps going without any problems. I haven't power cycled the hanged one from the last case (shown in logs), and the other one has been successfully running ever since, just as if zway couldn't handle both of them.
Also, like I said, I already have the latest firmware (3.1.4).
So please advise, what to do to solve this? Like I said, it does seem like this is zway issue, and I'm sure Heatit will say the same unless you can point something that individual devices does against zwave protocol.
samuli_jarvela
Any ideas how to solve this?
I left the other unit running after #23 dropped out, and the other was running successfully for a month until dropped out few days ago. With both of them connected they have never lasted this long, so I think this indicates pretty clearly that there is something in the zway that waits to be happening, and having more than one unit increases the odds very much.
I did also contact Heatit support, and they stated that they are not aware of this issue, so it also supports the claim that its the zway controller that is misbehaving.
Below are the logs for the second unit dropping out (#22). It's again the same thing, nonce reports are not getting through and eventually controller marks the device as failed.
Please tell me what else is there I can provide for you to solve this issue, this really is a deal breaker for me as it makes zway pretty unusable as a zwave controller if devices are lost in matter of days or weeks
[2021-07-17 10:00:21.855] [D] [zway] RECEIVED: ( 01 04 01 13 01 E8 )
[2021-07-17 10:00:21.855] [D] [zway] SENT ACK
[2021-07-17 10:00:21.855] [D] [zway] Delivered to Z-Wave stack
[2021-07-17 10:00:28.809] [D] [zway] RECEIVED: ( 01 18 00 13 62 01 02 B7 00 7F 7F 7F 7F 7F 01 01 07 00 00 00 00 02 14 10 16 4A )
[2021-07-17 10:00:28.810] [D] [zway] SENT ACK
[2021-07-17 10:00:28.810] [I] [zway] Job 0x13 (Nonce Get): Not delivered to recipient
[2021-07-17 10:00:28.810] [D] [zway] SENDING (cb 0x63): ( 01 09 00 13 16 02 98 40 25 63 6F )
[2021-07-17 10:00:28.814] [D] [zway] RECEIVED ACK
[2021-07-17 10:00:28.818] [D] [zway] RECEIVED: ( 01 04 01 13 01 E8 )
[2021-07-17 10:00:28.818] [D] [zway] SENT ACK
[2021-07-17 10:00:28.818] [D] [zway] Delivered to Z-Wave stack
[2021-07-17 10:00:29.810] [D] [zway] Job 0x13: deleted from queue
[2021-07-17 10:00:35.840] [D] [zway] RECEIVED: ( 01 18 00 13 63 01 02 BE 00 7F 7F 7F 7F 7F 01 01 07 00 00 00 00 02 11 03 16 54 )
[2021-07-17 10:00:35.841] [D] [zway] SENT ACK
[2021-07-17 10:00:35.841] [I] [zway] Job 0x13 (Nonce Get): Not delivered to recipient
[2021-07-17 10:00:35.841] [I] [zway] Job 0x13 (Nonce Get): Removing job due to too much retransmitions
[2021-07-17 10:00:35.841] [I] [zway] Adding job: Check if node is failed
[2021-07-17 10:00:35.841] [D] [zway] Job 0x13 (Nonce Get): fail
[2021-07-17 10:00:35.841] [I] [zway] Node 22:0 CC Security: sending Nonce Get
[2021-07-17 10:00:35.841] [D] [zway] SETDATA devices.22.instances.0.commandClasses.152.data.rNonceAckWait = **********
[2021-07-17 10:00:35.842] [I] [zway] Adding job: Nonce Get
[2021-07-17 10:00:35.842] [I] [zway] Removing job: Nonce Get
[2021-07-17 10:00:35.842] [D] [zway] SENDING: ( 01 04 00 62 16 8F )
[2021-07-17 10:00:35.844] [D] [zway] RECEIVED ACK
[2021-07-17 10:00:35.844] [D] [zway] RECEIVED: ( 01 04 01 62 01 99 )
[2021-07-17 10:00:35.844] [D] [zway] SENT ACK
[2021-07-17 10:00:35.844] [D] [zway] SETDATA devices.22.data.isFailed = True
[2021-07-17 10:00:35.844] [I] [zway] Job 0x62 (Check if node is failed): Node 22 is failed
[2021-07-17 10:00:35.844] [D] [zway] Job 0x62 (Check if node is failed): success
[2021-07-17 10:00:35.844] [D] [zway] SETDATA devices.22.data.failureCount = 1 (0x00000001)
[2021-07-17 10:00:35.844] [D] [zway] SETDATA devices.22.data.lastSendInternal = **********
[2021-07-17 10:00:35.844] [I] [zway] Removing job: Check if node is failed
[2021-07-17 10:00:53.677] [D] [zway] SENDING (cb 0x67): ( 01 09 00 13 16 02 98 40 25 67 6B )
[2021-07-17 10:00:53.682] [D] [zway] RECEIVED ACK
[2021-07-17 10:00:53.685] [D] [zway] RECEIVED: ( 01 04 01 13 01 E8 )
[2021-07-17 10:00:53.685] [D] [zway] SENT ACK
[2021-07-17 10:00:53.685] [D] [zway] Delivered to Z-Wave stack
[2021-07-17 10:00:56.145] [D] [zway] Job 0x13: deleted from queue
[2021-07-17 10:00:56.155] [D] [zway] Job 0x3b: deleted from queue
[2021-07-17 10:00:56.155] [D] [zway] Job 0x62: deleted from queue
[2021-07-17 10:01:00.760] [D] [zway] RECEIVED: ( 01 18 00 13 67 01 02 C3 00 7F 7F 7F 7F 7F 01 01 07 00 00 00 00 02 11 03 16 2D )
[2021-07-17 10:01:00.760] [D] [zway] SENT ACK
[2021-07-17 10:01:00.761] [I] [zway] Job 0x13 (Nonce Get): Not delivered to recipient
[2021-07-17 10:01:00.761] [D] [zway] SENDING (cb 0x68): ( 01 09 00 13 16 02 98 40 25 68 64 )
[2021-07-17 10:01:00.765] [D] [zway] RECEIVED ACK
[2021-07-17 10:01:00.769] [D] [zway] RECEIVED: ( 01 04 01 13 01 E8 )
[2021-07-17 10:01:00.769] [D] [zway] SENT ACK
[2021-07-17 10:01:00.769] [D] [zway] Delivered to Z-Wave stack
[2021-07-17 10:01:08.280] [D] [zway] RECEIVED: ( 01 18 00 13 68 01 02 EF 00 7F 7F 7F 7F 7F 01 01 07 00 00 00 00 02 11 03 16 0E )
[2021-07-17 10:01:08.281] [D] [zway] SENT ACK
[2021-07-17 10:01:08.281] [I] [zway] Job 0x13 (Nonce Get): Not delivered to recipient
[2021-07-17 10:01:08.281] [I] [zway] Job 0x13 (Nonce Get): Removing job due to too much retransmitions
[2021-07-17 10:01:08.281] [D] [zway] SETDATA devices.22.data.failureCount = 2 (0x00000002)
[2021-07-17 10:01:08.282] [D] [zway] SETDATA devices.22.data.lastSendInternal = **********
[2021-07-17 10:01:08.282] [D] [zway] Job 0x13 (Nonce Get): fail
[2021-07-17 10:01:08.282] [I] [zway] Node 22:0 CC Security: sending Nonce Get
[2021-07-17 10:01:08.282] [D] [zway] SETDATA devices.22.instances.0.commandClasses.152.data.rNonceAckWait = **********
[2021-07-17 10:01:08.282] [I] [zway] Adding job: Nonce Get
[2021-07-17 10:01:08.282] [I] [zway] Removing job: Nonce Get