CT100 Thermostat on Z-Way v2.0.1-rc12
The intervue completes. However the device is only properly controllable through the old "blueui". When I use the new expert gui, or home automation it doesn't function correctly. For example in the expert GUI adjusting the temperature sents the Thermostat mode to Heat. I noticed in the log files that old blueui used commandClass.64 for this while the new expertgui used commandClass.67. Please help!
Re: CT100 Thermostat on Z-Way v2.0.1-rc12
Next release candidate will have a more complete new Expert interface. You have to live with good old blue for a while. It is still a rc you now
Now running v2.0.1-rc37 and not only has this issue not been resolved, now the old-blue GUI that worked is gone! This should be considered a severe issue. Placing a HVAC unit in heat unexpectedly can lead to dangerous results. HVAC units that use heat strip coils, that are normally never maintained in warmer environments, when unexpectedly engaged can make the facility fill with smoke, it's a fire hazard. It's beggin for a lawsuit, especially since so easy to do from your Android and iOS app, the user will just think they just raised or lowered the temperate. I know this is a RC, however may I suggest, that if you don't plan to fix this, you remove the ability manage the thermostat from the GUI before removing the RC tag.pz1 wrote:Next release candidate will have a more complete new Expert interface. You have to live with good old blue for a while. It is still a rc you now
What is the problem with this CT100? Please describe it again in details, so we can fix it.
The device is not available in Europe, so it is hard to test.
When changing the temperature (in Celsius). The mode changes from to heat, for example I go to change the temperature from 23 to 22 degrees, the mode changes to heat. In February when I looked at it last, It only worked in the old "blueui". The new Expert UI, HomeAutomation used a different commandClass than the old blueGUI.
I can get you log files of both set of commands being issued... however can I copy the old BlueGUI from old of the backup installs into the latest RC? Do I have to downgrade?
In addition to the mode being set to heat, the temperature is changed to 18C (regardless if I increment up or down). Seems to be calling the wrong command class (67), when it should be using (64).
I can set the temperature properly in my scripts like this:
http://$zwaveMeSrv/ZWaveAPI/Run/devices[11].instances[0].commandClasses[67].Set(2,$temp)
[2015-06-27 00:18:02.598] [I] [zway] Adding job: ThermostatMode Set
[2015-06-27 00:18:02.600] [I] [zway] Adding job: ThermostatMode Get
[2015-06-27 00:18:02.611] [D] [zway] SENDING (cb 0xc9): ( 01 0A 00 13 0B 03 40 01 01 05 C9 62 )
[2015-06-27 00:18:02.614] [D] [zway] RECEIVED ACK
[2015-06-27 00:18:02.617] [D] [zway] RECEIVED: ( 01 04 01 13 01 E8 )
[2015-06-27 00:18:02.618] [D] [zway] SENT ACK
[2015-06-27 00:18:02.619] [D] [zway] Delivered to Z-Wave stack
[2015-06-27 00:18:03.812] [D] [zway] RECEIVED: ( 01 05 00 13 C9 00 20 )
[2015-06-27 00:18:03.813] [D] [zway] SENT ACK
[2015-06-27 00:18:03.814] [I] [zway] Job 0x13 (ThermostatMode Set): Delivered
[2015-06-27 00:18:03.815] [D] [zway] SETDATA devices.11.data.lastPacketInfo.delivered = True
[2015-06-27 00:18:03.817] [D] [zway] SETDATA devices.11.data.lastPacketInfo.packetLength = 6 (0x00000006)
[2015-06-27 00:18:03.818] [D] [zway] SETDATA devices.11.data.lastPacketInfo.deliveryTime = 1194 (0x000004aa)
[2015-06-27 00:18:03.819] [D] [zway] SETDATA devices.11.data.lastPacketInfo = **********
[2015-06-27 00:18:03.820] [D] [zway] SendData Response with callback 0xc9 received: received by recipient
[2015-06-27 00:18:03.822] [D] [zway] SETDATA devices.11.data.lastSend = 17272426 (0x01078e6a)
[2015-06-27 00:18:03.823] [D] [zway] Job 0x13 (ThermostatMode Set): success
[2015-06-27 00:18:03.824] [I] [zway] Removing job: ThermostatMode Set
[2015-06-27 00:18:03.876] [D] [zway] SENDING (cb 0xca): ( 01 09 00 13 0B 02 40 02 05 CA 61 )
[2015-06-27 00:18:03.879] [D] [zway] RECEIVED ACK
[2015-06-27 00:18:03.882] [D] [zway] RECEIVED: ( 01 04 01 13 01 E8 )
[2015-06-27 00:18:03.883] [D] [zway] SENT ACK
[2015-06-27 00:18:03.885] [D] [zway] Delivered to Z-Wave stack
[2015-06-27 00:18:05.077] [D] [zway] RECEIVED: ( 01 05 00 13 CA 00 23 )
[2015-06-27 00:18:05.078] [D] [zway] SENT ACK
[2015-06-27 00:18:05.078] [I] [zway] Job 0x13 (ThermostatMode Get): Delivered
[2015-06-27 00:18:05.080] [D] [zway] SETDATA devices.11.data.lastPacketInfo.delivered = True
[2015-06-27 00:18:05.081] [D] [zway] SETDATA devices.11.data.lastPacketInfo.packetLength = 5 (0x00000005)
[2015-06-27 00:18:05.083] [D] [zway] SETDATA devices.11.data.lastPacketInfo.deliveryTime = 1195 (0x000004ab)
[2015-06-27 00:18:05.084] [D] [zway] SETDATA devices.11.data.lastPacketInfo = **********
[2015-06-27 00:18:05.085] [D] [zway] SendData Response with callback 0xca received: received by recipient
[2015-06-27 00:18:05.086] [D] [zway] SETDATA devices.11.data.lastSend = 17272550 (0x01078ee6)
[2015-06-27 00:18:05.087] [D] [zway] Job 0x13 (ThermostatMode Get): success
[2015-06-27 00:18:05.089] [I] [zway] Removing job: ThermostatMode Get
[2015-06-27 00:18:05.161] [D] [zway] RECEIVED: ( 01 09 00 04 00 0B 03 40 03 01 B8 )
[2015-06-27 00:18:05.162] [D] [zway] SENT ACK
[2015-06-27 00:18:05.162] [D] [zway] SETDATA devices.11.data.lastReceived = 0 (0x00000000)
[2015-06-27 00:18:05.162] [D] [zway] SETDATA devices.11.instances.0.commandClasses.64.data.mode = 1 (0x00000001)
In your log I see only "ThermostatMode.Set(Heat) command, not temperature selection seen
See the problem now. I'm not selecting the Heat command, just adjusting the temperature, the same if adjusting up or down.PoltoS wrote:In your log I see only "ThermostatMode.Set(Heat) command, not temperature selection seen
In my earlier post I meant the wrong command class is (64). Command class (67) is what I use in my scripts, and what the defunct bluegui used as well. Not sure why temperature changes to 18C, I'm guessing it's because the command is being issued with some out of bounds data that causes the unit to switch to 18C??? I'm not the expert.
The CT100 is certified Z-Wave device and listed under the zwave database and the Expert User Interface is included in the certification. Have any thermostats been recently tested on the RC builds? Can this issue be duplicated with other vendors hardware?
No difference after reinterview. I have attached partial logs of the re-interview, there's some other chatter in there, it is device 11.
After reinterview, again changing the temperature...
[2015-06-27 23:34:08.347] [I] [zway] Adding job: ThermostatMode Set
[2015-06-27 23:34:08.348] [I] [zway] Adding job: ThermostatMode Get
[2015-06-27 23:34:08.354] [D] [zway] SENDING (cb 0x22): ( 01 0A 00 13 0B 03 40 01 01 05 22 89 )
[2015-06-27 23:34:08.356] [D] [zway] RECEIVED ACK
[2015-06-27 23:34:08.360] [D] [zway] RECEIVED: ( 01 04 01 13 01 E8 )
[2015-06-27 23:34:08.361] [D] [zway] SENT ACK
[2015-06-27 23:34:08.362] [D] [zway] Delivered to Z-Wave stack
[2015-06-27 23:34:09.555] [D] [zway] RECEIVED: ( 01 05 00 13 22 00 CB )
[2015-06-27 23:34:09.556] [D] [zway] SENT ACK
[2015-06-27 23:34:09.557] [I] [zway] Job 0x13 (ThermostatMode Set): Delivered
[2015-06-27 23:34:09.558] [D] [zway] SETDATA devices.11.data.lastPacketInfo.delivered = True
[2015-06-27 23:34:09.559] [D] [zway] SETDATA devices.11.data.lastPacketInfo.packetLength = 6 (0x00000006)
[2015-06-27 23:34:09.560] [D] [zway] SETDATA devices.11.data.lastPacketInfo.deliveryTime = 1195 (0x000004ab)
[2015-06-27 23:34:09.562] [D] [zway] SETDATA devices.11.data.lastPacketInfo = **********
[2015-06-27 23:34:09.563] [D] [zway] SendData Response with callback 0x22 received: received by recipient
[2015-06-27 23:34:09.564] [D] [zway] SETDATA devices.11.data.lastSend = 25418882 (0x0183dc82)
[2015-06-27 23:34:09.565] [D] [zway] Job 0x13 (ThermostatMode Set): success
[2015-06-27 23:34:09.566] [I] [zway] Removing job: ThermostatMode Set
[2015-06-27 23:34:09.630] [D] [zway] SENDING (cb 0x23): ( 01 09 00 13 0B 02 40 02 05 23 88 )
[2015-06-27 23:34:09.632] [D] [zway] RECEIVED ACK
[2015-06-27 23:34:09.635] [D] [zway] RECEIVED: ( 01 04 01 13 01 E8 )
[2015-06-27 23:34:09.636] [D] [zway] SENT ACK
[2015-06-27 23:34:09.637] [D] [zway] Delivered to Z-Wave stack
[2015-06-27 23:34:10.829] [D] [zway] RECEIVED: ( 01 05 00 13 23 00 CA )
[2015-06-27 23:34:10.830] [D] [zway] SENT ACK
[2015-06-27 23:34:10.831] [I] [zway] Job 0x13 (ThermostatMode Get): Delivered
[2015-06-27 23:34:10.832] [D] [zway] SETDATA devices.11.data.lastPacketInfo.delivered = True
[2015-06-27 23:34:10.834] [D] [zway] SETDATA devices.11.data.lastPacketInfo.packetLength = 5 (0x00000005)
[2015-06-27 23:34:10.834] [D] [zway] SETDATA devices.11.data.lastPacketInfo.deliveryTime = 1194 (0x000004aa)
[2015-06-27 23:34:10.836] [D] [zway] SETDATA devices.11.data.lastPacketInfo = **********
[2015-06-27 23:34:10.837] [D] [zway] SendData Response with callback 0x23 received: received by recipient
[2015-06-27 23:34:10.838] [D] [zway] SETDATA devices.11.data.lastSend = 25419006 (0x0183dcfe)
[2015-06-27 23:34:10.839] [D] [zway] Job 0x13 (ThermostatMode Get): success
[2015-06-27 23:34:10.840] [I] [zway] Removing job: ThermostatMode Get
[2015-06-27 23:34:11.065] [D] [zway] RECEIVED: ( 01 09 00 04 00 0B 03 40 03 01 B8 )
[2015-06-27 23:34:11.066] [D] [zway] SENT ACK
[2015-06-27 23:34:11.067] [D] [zway] SETDATA devices.11.data.lastReceived = 0 (0x00000000)
[2015-06-27 23:34:11.068] [D] [zway] SETDATA devices.11.instances.0.commandClasses.64.data.mode = 1 (0x00000001)
Couldn't attach, extension not allowed error regardless of the extension, so here's the interview data.
[2015-06-27 23:19:15.237] [I] [zway] Adding job: Basic Version Get
[2015-06-27 23:19:15.238] [I] [zway] Adding job: SensorMultilevel Version Get
[2015-06-27 23:19:15.240] [I] [zway] Adding job: ThermostatMode Version Get
[2015-06-27 23:19:15.241] [I] [zway] Adding job: ThermostatOperatingState Version Get
[2015-06-27 23:19:15.242] [I] [zway] Adding job: ThermostatFanMode Version Get
[2015-06-27 23:19:15.243] [I] [zway] Adding job: MultiChannel Version Get
[2015-06-27 23:19:15.244] [I] [zway] Adding job: Configuration Version Get
[2015-06-27 23:19:15.245] [I] [zway] Adding job: ManufacturerSpecific Version Get
[2015-06-27 23:19:15.246] [I] [zway] Adding job: Battery Version Get
[2015-06-27 23:19:15.248] [I] [zway] Adding job: Clock Version Get
[2015-06-27 23:19:15.249] [I] [zway] Adding job: Association Version Get
[2015-06-27 23:19:15.250] [I] [zway] Adding job: Version Version Get
[2015-06-27 23:19:15.251] [I] [zway] Adding job: Indicator Version Get
[2015-06-27 23:19:15.252] [I] [zway] Adding job: ThermostatSetPoint Version Get
[2015-06-27 23:19:15.253] [D] [zway] SENDING (cb 0xfd): ( 01 0A 00 13 0B 03 86 13 20 05 FD A3 )
[2015-06-27 23:19:15.256] [D] [zway] RECEIVED ACK
[2015-06-27 23:19:15.260] [D] [zway] RECEIVED: ( 01 04 01 13 01 E8 )
[2015-06-27 23:19:15.260] [D] [zway] SENT ACK
[2015-06-27 23:19:15.262] [D] [zway] Delivered to Z-Wave stack
[2015-06-27 23:19:16.459] [D] [zway] RECEIVED: ( 01 05 00 13 FD 00 14 )
[2015-06-27 23:19:16.460] [D] [zway] SENT ACK
[2015-06-27 23:19:16.461] [I] [zway] Job 0x13 (Basic Version Get): Delivered
[2015-06-27 23:19:16.462] [D] [zway] SETDATA devices.11.data.lastPacketInfo.delivered = True
[2015-06-27 23:19:16.463] [D] [zway] SETDATA devices.11.data.lastPacketInfo.packetLength = 6 (0x00000006)
[2015-06-27 23:19:16.464] [D] [zway] SETDATA devices.11.data.lastPacketInfo.deliveryTime = 1199 (0x000004af)
[2015-06-27 23:19:16.466] [D] [zway] SETDATA devices.11.data.lastPacketInfo = **********
[2015-06-27 23:19:16.467] [D] [zway] SendData Response with callback 0xfd received: received by recipient
[2015-06-27 23:19:16.468] [D] [zway] SETDATA devices.11.data.lastSend = 25332044 (0x0182894c)
[2015-06-27 23:19:16.469] [D] [zway] Job 0x13 (Basic Version Get): success
[2015-06-27 23:19:16.470] [I] [zway] Removing job: Basic Version Get
[2015-06-27 23:19:16.502] [D] [zway] RECEIVED: ( 01 0A 00 04 00 0B 04 86 14 20 01 4D )
[2015-06-27 23:19:16.503] [D] [zway] SENT ACK
[2015-06-27 23:19:16.503] [D] [zway] SETDATA devices.11.data.lastReceived = 0 (0x00000000)
[2015-06-27 23:19:16.505] [I] [zway] Node 11:0 CC Version: Basic is v1
[2015-06-27 23:19:16.506] [D] [zway] SETDATA devices.11.instances.0.commandClasses.32.data.version = 1 (0x00000001)
[2015-06-27 23:19:16.533] [D] [zway] SENDING (cb 0xfe): ( 01 0A 00 13 0B 03 86 13 31 05 FE B1 )
[2015-06-27 23:19:16.539] [D] [zway] RECEIVED ACK
[2015-06-27 23:19:16.543] [D] [zway] RECEIVED: ( 01 04 01 13 01 E8 )
[2015-06-27 23:19:16.543] [D] [zway] SENT ACK
[2015-06-27 23:19:16.544] [D] [zway] Delivered to Z-Wave stack
[2015-06-27 23:19:17.738] [D] [zway] RECEIVED: ( 01 05 00 13 FE 00 17 )
[2015-06-27 23:19:17.739] [D] [zway] SENT ACK
[2015-06-27 23:19:17.740] [I] [zway] Job 0x13 (SensorMultilevel Version Get): Delivered
[2015-06-27 23:19:17.741] [D] [zway] SETDATA devices.11.data.lastPacketInfo.delivered = True
[2015-06-27 23:19:17.742] [D] [zway] SETDATA devices.11.data.lastPacketInfo.packetLength = 6 (0x00000006)
[2015-06-27 23:19:17.743] [D] [zway] SETDATA devices.11.data.lastPacketInfo.deliveryTime = 1195 (0x000004ab)
[2015-06-27 23:19:17.745] [D] [zway] SETDATA devices.11.data.lastPacketInfo = **********
[2015-06-27 23:19:17.746] [D] [zway] SendData Response with callback 0xfe received: received by recipient
[2015-06-27 23:19:17.747] [D] [zway] SETDATA devices.11.data.lastSend = 25332168 (0x018289c8)
[2015-06-27 23:19:17.748] [D] [zway] Job 0x13 (SensorMultilevel Version Get): success
[2015-06-27 23:19:17.749] [I] [zway] Removing job: SensorMultilevel Version Get
[2015-06-27 23:19:17.760] [D] [zway] RECEIVED: ( 01 09 00 04 00 09 03 80 03 00 7B )
[2015-06-27 23:19:17.761] [D] [zway] SENT ACK
[2015-06-27 23:19:17.762] [D] [zway] SETDATA devices.9.data.lastReceived = 0 (0x00000000)
[2015-06-27 23:19:17.763] [D] [zway] SETDATA devices.9.instances.0.commandClasses.128.data.history.0 = 1435461557 (0x558f67b5)
[2015-06-27 23:19:17.764] [D] [zway] SETDATA devices.9.instances.0.commandClasses.128.data.last = 0 (0x00000000)
[2015-06-27 23:19:17.782] [D] [zway] RECEIVED: ( 01 0A 00 04 00 0B 04 86 14 31 02 5F )
[2015-06-27 23:19:17.783] [D] [zway] SENT ACK
[2015-06-27 23:19:17.784] [D] [zway] SETDATA devices.11.data.lastReceived = 0 (0x00000000)
[2015-06-27 23:19:17.786] [I] [zway] Node 11:0 CC Version: SensorMultilevel is v2
[2015-06-27 23:19:17.787] [D] [zway] SETDATA devices.11.instances.0.commandClasses.49.data.version = 2 (0x00000002)
[2015-06-27 23:19:17.788] [D] [zway] SETDATA devices.11.instances.1.commandClasses.49.data.version = 2 (0x00000002)
[2015-06-27 23:19:17.789] [D] [zway] SETDATA devices.11.instances.2.commandClasses.49.data.version = 2 (0x00000002)
[2015-06-27 23:19:17.801] [D] [zway] RECEIVED: ( 01 0C 00 04 00 09 06 31 05 03 0A 00 08 CD )
[2015-06-27 23:19:17.802] [D] [zway] SENT ACK
[2015-06-27 23:19:17.803] [D] [zway] SETDATA devices.9.data.lastReceived = 0 (0x00000000)
[2015-06-27 23:19:17.804] [D] [zway] SETDATA devices.9.instances.0.commandClasses.49.data.3.deviceScale = 1 (0x00000001)
[2015-06-27 23:19:17.806] [D] [zway] SETDATA devices.9.instances.0.commandClasses.49.data.3.scale = 1 (0x00000001)
[2015-06-27 23:19:17.807] [D] [zway] SETDATA devices.9.instances.0.commandClasses.49.data.3.val = 8.000000
[2015-06-27 23:19:17.810] [D] [zway] SETDATA devices.9.instances.0.commandClasses.49.data.3.scaleString = "Lux"
[2015-06-27 23:19:17.811] [D] [zway] SETDATA devices.9.instances.0.commandClasses.49.data.3 = Empty
[2015-06-27 23:19:17.821] [D] [zway] SENDING (cb 0x01): ( 01 0A 00 13 0B 03 86 13 40 05 01 3F )
[2015-06-27 23:19:17.823] [D] [zway] RECEIVED ACK
[2015-06-27 23:19:17.827] [D] [zway] RECEIVED: ( 01 04 01 13 01 E8 )
[2015-06-27 23:19:17.828] [D] [zway] SENT ACK
[2015-06-27 23:19:17.829] [D] [zway] Delivered to Z-Wave stack
[2015-06-27 23:19:19.118] [D] [zway] RECEIVED: ( 01 05 00 13 01 00 E8 )
[2015-06-27 23:19:19.119] [D] [zway] SENT ACK
[2015-06-27 23:19:19.119] [I] [zway] Job 0x13 (ThermostatMode Version Get): Delivered
[2015-06-27 23:19:19.120] [D] [zway] SETDATA devices.11.data.lastPacketInfo.delivered = True
[2015-06-27 23:19:19.122] [D] [zway] SETDATA devices.11.data.lastPacketInfo.packetLength = 6 (0x00000006)
[2015-06-27 23:19:19.123] [D] [zway] SETDATA devices.11.data.lastPacketInfo.deliveryTime = 1291 (0x0000050b)
[2015-06-27 23:19:19.124] [D] [zway] SETDATA devices.11.data.lastPacketInfo = **********
[2015-06-27 23:19:19.125] [D] [zway] SendData Response with callback 0x01 received: received by recipient
[2015-06-27 23:19:19.126] [D] [zway] SETDATA devices.11.data.lastSend = 25332300 (0x01828a4c)
[2015-06-27 23:19:19.127] [D] [zway] Job 0x13 (ThermostatMode Version Get): success
[2015-06-27 23:19:19.128] [I] [zway] Removing job: ThermostatMode Version Get
[2015-06-27 23:19:19.150] [D] [zway] RECEIVED: ( 01 0C 00 04 00 09 06 31 05 05 01 43 00 8B )
[2015-06-27 23:19:19.151] [D] [zway] SENT ACK
[2015-06-27 23:19:19.152] [D] [zway] SETDATA devices.9.data.lastReceived = 0 (0x00000000)
[2015-06-27 23:19:19.153] [D] [zway] SETDATA devices.9.instances.0.commandClasses.49.data.5.deviceScale = 0 (0x00000000)
[2015-06-27 23:19:19.154] [D] [zway] SETDATA devices.9.instances.0.commandClasses.49.data.5.scale = 0 (0x00000000)
[2015-06-27 23:19:19.155] [D] [zway] SETDATA devices.9.instances.0.commandClasses.49.data.5.val = 67.000000
[2015-06-27 23:19:19.159] [D] [zway] SETDATA devices.9.instances.0.commandClasses.49.data.5.scaleString = "%"
[2015-06-27 23:19:19.160] [D] [zway] SETDATA devices.9.instances.0.commandClasses.49.data.5 = Empty
[2015-06-27 23:19:19.188] [D] [zway] RECEIVED: ( 01 0C 00 04 00 09 06 31 05 01 2A 03 15 F1 )
[2015-06-27 23:19:19.189] [D] [zway] SENT ACK
[2015-06-27 23:19:19.190] [D] [zway] SETDATA devices.9.data.lastReceived = 0 (0x00000000)
[2015-06-27 23:19:19.192] [D] [zway] SETDATA devices.9.instances.0.commandClasses.49.data.1.deviceScale = 1 (0x00000001)
[2015-06-27 23:19:19.193] [D] [zway] SETDATA devices.9.instances.0.commandClasses.49.data.1.val = 26.100000
[2015-06-27 23:19:19.195] [D] [zway] SETDATA devices.9.instances.0.commandClasses.49.data.1.scale = 0 (0x00000000)
[2015-06-27 23:19:19.198] [D] [zway] SETDATA devices.9.instances.0.commandClasses.49.data.1.scaleString = "°C"
[2015-06-27 23:19:19.202] [D] [zway] SETDATA devices.9.instances.0.commandClasses.49.data.1 = Empty
[2015-06-27 23:19:19.203] [D] [zway] SENDING (cb 0x02): ( 01 0A 00 13 0B 03 86 13 42 05 02 3E )
[2015-06-27 23:19:19.209] [W] [zway] Received SOF, while awaiting ACK
[2015-06-27 23:19:19.210] [D] [zway] RECEIVED: ( 01 08 00 04 00 09 02 84 07 7B )
[2015-06-27 23:19:19.211] [D] [zway] SENT ACK
[2015-06-27 23:19:19.213] [D] [zway] SETDATA devices.9.data.lastReceived = 0 (0x00000000)
[2015-06-27 23:19:19.214] [I] [zway] Node 9:0 CC Wakeup: Wakeup notification
[2015-06-27 23:19:19.214] [D] [zway] SETDATA devices.9.instances.0.commandClasses.132.data.lastWakeup = 1435461559 (0x558f67b7)
[2015-06-27 23:19:19.216] [D] [zway] SETDATA devices.9.data.isAwake = True
[2015-06-27 23:19:19.217] [D] [zway] SETDATA devices.9.data.lastSend = 25332307 (0x01828a53)
[2015-06-27 23:19:19.218] [D] [zway] SETDATA devices.9.data.lastNonceGet = 25331307 (0x0182866b)
[2015-06-27 23:19:19.219] [D] [zway] Running wakeup handler for node 9
[2015-06-27 23:19:19.220] [D] [zway] SETDATA devices.9.instances.0.commandClasses.132.data.lastSleep = 1435461559 (0x558f67b7)
[2015-06-27 23:19:19.221] [I] [zway] Node 9:0 CC Wakeup: Send node to sleep
[2015-06-27 23:19:19.222] [I] [zway] Adding job: Wakeup Sleep
[2015-06-27 23:19:19.224] [D] [zway] RECEIVED CAN
[2015-06-27 23:19:19.266] [W] [zway] Received SOF, while awaiting ACK
[2015-06-27 23:19:19.267] [D] [zway] RECEIVED: ( 01 0A 00 04 00 0B 04 86 14 40 02 2E )
[2015-06-27 23:19:19.267] [D] [zway] SENT ACK
[2015-06-27 23:19:19.269] [D] [zway] SETDATA devices.11.data.lastReceived = 0 (0x00000000)
[2015-06-27 23:19:19.270] [I] [zway] Node 11:0 CC Version: ThermostatMode is v2
[2015-06-27 23:19:19.271] [D] [zway] SETDATA devices.11.instances.0.commandClasses.64.data.version = 2 (0x00000002)
[2015-06-27 23:19:19.720] [I] [zway] Job 0x13 (ThermostatOperatingState Version Get): No ACK received before timeout
[2015-06-27 23:19:19.722] [D] [zway] SENDING (cb 0x02): ( 01 0A 00 13 0B 03 86 13 42 05 02 3E )
[2015-06-27 23:19:19.724] [D] [zway] RECEIVED ACK
[2015-06-27 23:19:19.728] [D] [zway] RECEIVED: ( 01 04 01 13 01 E8 )
[2015-06-27 23:19:19.728] [D] [zway] SENT ACK
[2015-06-27 23:19:19.729] [D] [zway] Delivered to Z-Wave stack
[2015-06-27 23:19:20.169] [I] [zway] Adding job: SwitchMultilevel Get
[2015-06-27 23:19:20.923] [D] [zway] RECEIVED: ( 01 05 00 13 02 00 EB )
[2015-06-27 23:19:20.924] [D] [zway] SENT ACK
[2015-06-27 23:19:20.925] [I] [zway] Job 0x13 (ThermostatOperatingState Version Get): Delivered
[2015-06-27 23:19:20.926] [D] [zway] SETDATA devices.11.data.lastPacketInfo.delivered = True
[2015-06-27 23:19:20.927] [D] [zway] SETDATA devices.11.data.lastPacketInfo.packetLength = 6 (0x00000006)
[2015-06-27 23:19:20.929] [D] [zway] SETDATA devices.11.data.lastPacketInfo.deliveryTime = 1195 (0x000004ab)
[2015-06-27 23:19:20.930] [D] [zway] SETDATA devices.11.data.lastPacketInfo = **********
[2015-06-27 23:19:20.931] [D] [zway] SendData Response with callback 0x02 received: received by recipient
[2015-06-27 23:19:20.932] [D] [zway] SETDATA devices.11.data.lastSend = 25332467 (0x01828af3)
[2015-06-27 23:19:20.933] [D] [zway] Job 0x13 (ThermostatOperatingState Version Get): success
[2015-06-27 23:19:20.934] [I] [zway] Removing job: ThermostatOperatingState Version Get
[2015-06-27 23:19:20.935] [D] [zway] SENDING (cb 0x03): ( 01 09 00 13 09 02 84 08 05 03 64 )
[2015-06-27 23:19:20.938] [D] [zway] RECEIVED ACK
[2015-06-27 23:19:20.941] [D] [zway] RECEIVED: ( 01 04 01 13 01 E8 )
[2015-06-27 23:19:20.942] [D] [zway] SENT ACK
[2015-06-27 23:19:20.942] [D] [zway] Delivered to Z-Wave stack
[2015-06-27 23:19:20.953] [D] [zway] RECEIVED: ( 01 05 00 13 03 00 EA )
[2015-06-27 23:19:20.954] [D] [zway] SENT ACK
[2015-06-27 23:19:20.955] [I] [zway] Job 0x13 (Wakeup Sleep): Delivered
[2015-06-27 23:19:20.956] [D] [zway] SETDATA devices.9.data.lastPacketInfo.delivered = True
[2015-06-27 23:19:20.957] [D] [zway] SETDATA devices.9.data.lastPacketInfo.packetLength = 5 (0x00000005)
[2015-06-27 23:19:20.958] [D] [zway] SETDATA devices.9.data.lastPacketInfo.deliveryTime = 12 (0x0000000c)
[2015-06-27 23:19:20.959] [D] [zway] SETDATA devices.9.data.lastPacketInfo = **********
[2015-06-27 23:19:20.961] [D] [zway] SendData Response with callback 0x03 received: received by recipient
[2015-06-27 23:19:20.962] [D] [zway] SETDATA devices.9.data.lastSend = 25332470 (0x01828af6)
[2015-06-27 23:19:20.963] [D] [zway] Job 0x13 (Wakeup Sleep): success
[2015-06-27 23:19:20.964] [D] [zway] SETDATA devices.9.data.isAwake = False
[2015-06-27 23:19:20.965] [D] [zway] Sending the queue for node 9 into sleep
[2015-06-27 23:19:20.966] [I] [zway] Removing job: Wakeup Sleep
[2015-06-27 23:19:20.967] [D] [zway] SENDING (cb 0x04): ( 01 09 00 13 07 02 26 02 25 04 E5 )
[2015-06-27 23:19:20.970] [D] [zway] RECEIVED ACK
[2015-06-27 23:19:20.973] [D] [zway] RECEIVED: ( 01 04 01 13 01 E8 )
[2015-06-27 23:19:20.974] [D] [zway] SENT ACK
[2015-06-27 23:19:20.975] [D] [zway] Delivered to Z-Wave stack
[2015-06-27 23:19:21.008] [D] [zway] RECEIVED: ( 01 05 00 13 04 00 ED )
[2015-06-27 23:19:21.009] [D] [zway] SENT ACK
[2015-06-27 23:19:21.010] [I] [zway] Job 0x13 (SwitchMultilevel Get): Delivered
[2015-06-27 23:19:21.011] [D] [zway] SETDATA devices.7.data.lastPacketInfo.delivered = True
[2015-06-27 23:19:21.012] [D] [zway] SETDATA devices.7.data.lastPacketInfo.packetLength = 5 (0x00000005)
[2015-06-27 23:19:21.014] [D] [zway] SETDATA devices.7.data.lastPacketInfo.deliveryTime = 36 (0x00000024)
[2015-06-27 23:19:21.015] [D] [zway] SETDATA devices.7.data.lastPacketInfo = **********
[2015-06-27 23:19:21.016] [D] [zway] SendData Response with callback 0x04 received: received by recipient
[2015-06-27 23:19:21.017] [D] [zway] SETDATA devices.7.data.lastSend = 25332475 (0x01828afb)
[2015-06-27 23:19:21.018] [D] [zway] Job 0x13 (SwitchMultilevel Get): success
[2015-06-27 23:19:21.018] [I] [zway] Removing job: SwitchMultilevel Get
[2015-06-27 23:19:21.020] [D] [zway] SENDING (cb 0x05): ( 01 0A 00 13 0B 03 86 13 44 05 05 3F )
[2015-06-27 23:19:21.023] [D] [zway] RECEIVED ACK
[2015-06-27 23:19:21.026] [D] [zway] RECEIVED: ( 01 04 01 13 01 E8 )
[2015-06-27 23:19:21.027] [D] [zway] SENT ACK
[2015-06-27 23:19:21.028] [D] [zway] Delivered to Z-Wave stack
[2015-06-27 23:19:21.095] [I] [zway] Adding job: SwitchMultilevel Get
[2015-06-27 23:19:21.146] [D] [zway] RECEIVED: ( 01 0A 00 04 00 0B 04 86 14 42 02 2C )
[2015-06-27 23:19:21.146] [D] [zway] SENT ACK
[2015-06-27 23:19:21.146] [D] [zway] SETDATA devices.11.data.lastReceived = 0 (0x00000000)
[2015-06-27 23:19:21.146] [I] [zway] Node 11:0 CC Version: ThermostatOperatingState is v2
[2015-06-27 23:19:21.147] [D] [zway] SETDATA devices.11.instances.0.commandClasses.66.data.version = 2 (0x00000002)
[2015-06-27 23:19:21.189] [D] [zway] RECEIVED: ( 01 0A 00 04 00 0B 04 86 14 42 02 2C )
[2015-06-27 23:19:21.189] [D] [zway] SENT ACK
[2015-06-27 23:19:21.190] [D] [zway] SETDATA devices.11.data.lastReceived = 0 (0x00000000)
[2015-06-27 23:19:21.190] [I] [zway] Node 11:0 CC Version: ThermostatOperatingState is v2
[2015-06-27 23:19:21.190] [D] [zway] SETDATA devices.11.instances.0.commandClasses.66.data.version = 2 (0x00000002)
[2015-06-27 23:19:23.455] [D] [zway] Job 0x13 (SwitchMultilevel Get): removing duplicate
[2015-06-27 23:19:24.491] [D] [zway] Job 0x13 (SwitchMultilevel Get): removing duplicate
[2015-06-27 23:19:27.109] [D] [zway] RECEIVED: ( 01 05 00 13 05 00 EC )
[2015-06-27 23:19:27.110] [D] [zway] SENT ACK
[2015-06-27 23:19:27.111] [I] [zway] Job 0x13 (ThermostatFanMode Version Get): Delivered
[2015-06-27 23:19:27.112] [D] [zway] SETDATA devices.11.data.lastPacketInfo.delivered = True
[2015-06-27 23:19:27.113] [D] [zway] SETDATA devices.11.data.lastPacketInfo.packetLength = 6 (0x00000006)
[2015-06-27 23:19:27.114] [D] [zway] SETDATA devices.11.data.lastPacketInfo.deliveryTime = 6079 (0x000017bf)
[2015-06-27 23:19:27.115] [D] [zway] SETDATA devices.11.data.lastPacketInfo = **********
[2015-06-27 23:19:27.117] [D] [zway] SendData Response with callback 0x05 received: received by recipient
[2015-06-27 23:19:27.118] [D] [zway] SETDATA devices.11.data.lastSend = 25333068 (0x01828d4c)
[2015-06-27 23:19:27.118] [D] [zway] Job 0x13 (ThermostatFanMode Version Get): success
[2015-06-27 23:19:27.119] [I] [zway] Removing job: ThermostatFanMode Version Get
[2015-06-27 23:19:27.122] [D] [zway] SENDING (cb 0x06): ( 01 09 00 13 07 02 26 02 25 06 E7 )
[2015-06-27 23:19:27.125] [D] [zway] RECEIVED ACK
[2015-06-27 23:19:27.127] [D] [zway] RECEIVED: ( 01 04 01 13 01 E8 )
[2015-06-27 23:19:27.128] [D] [zway] SENT ACK
[2015-06-27 23:19:27.129] [D] [zway] Delivered to Z-Wave stack
[2015-06-27 23:19:27.144] [D] [zway] RECEIVED: ( 01 0A 00 04 00 0B 04 86 14 44 01 29 )
[2015-06-27 23:19:27.145] [D] [zway] SENT ACK
[2015-06-27 23:19:27.146] [D] [zway] SETDATA devices.11.data.lastReceived = 0 (0x00000000)
[2015-06-27 23:19:27.147] [I] [zway] Node 11:0 CC Version: ThermostatFanMode is v1
[2015-06-27 23:19:27.148] [D] [zway] SETDATA devices.11.instances.0.commandClasses.68.data.version = 1 (0x00000001)
[2015-06-27 23:19:27.348] [D] [zway] RECEIVED: ( 01 0A 00 04 00 0B 04 86 14 44 01 29 )
[2015-06-27 23:19:27.349] [D] [zway] SENT ACK
[2015-06-27 23:19:27.350] [D] [zway] SETDATA devices.11.data.lastReceived = 0 (0x00000000)
[2015-06-27 23:19:27.351] [I] [zway] Node 11:0 CC Version: ThermostatFanMode is v1
[2015-06-27 23:19:27.352] [D] [zway] SETDATA devices.11.instances.0.commandClasses.68.data.version = 1 (0x00000001)
[2015-06-27 23:19:27.510] [D] [zway] RECEIVED: ( 01 05 00 13 06 00 EF )
[2015-06-27 23:19:27.520] [D] [zway] SENT ACK
[2015-06-27 23:19:27.522] [I] [zway] Job 0x13 (SwitchMultilevel Get): Delivered
[2015-06-27 23:19:27.523] [D] [zway] SETDATA devices.7.data.lastPacketInfo.delivered = True
[2015-06-27 23:19:27.524] [D] [zway] SETDATA devices.7.data.lastPacketInfo.packetLength = 5 (0x00000005)
[2015-06-27 23:19:27.525] [D] [zway] SETDATA devices.7.data.lastPacketInfo.deliveryTime = 393 (0x00000189)
[2015-06-27 23:19:27.526] [D] [zway] SETDATA devices.7.data.lastPacketInfo = **********
[2015-06-27 23:19:27.527] [D] [zway] SendData Response with callback 0x06 received: received by recipient
[2015-06-27 23:19:27.528] [D] [zway] SETDATA devices.7.data.lastSend = 25333106 (0x01828d72)
[2015-06-27 23:19:27.529] [D] [zway] Job 0x13 (SwitchMultilevel Get): success
[2015-06-27 23:19:27.531] [I] [zway] Removing job: SwitchMultilevel Get
[2015-06-27 23:19:27.533] [D] [zway] SENDING (cb 0x07): ( 01 0A 00 13 0B 03 86 13 60 05 07 19 )
[2015-06-27 23:19:27.536] [D] [zway] RECEIVED ACK
[2015-06-27 23:19:27.538] [D] [zway] RECEIVED: ( 01 04 01 13 01 E8 )
[2015-06-27 23:19:27.539] [D] [zway] SENT ACK
[2015-06-27 23:19:27.540] [D] [zway] Delivered to Z-Wave stack
[2015-06-27 23:19:27.555] [D] [zway] RECEIVED: ( 01 09 00 04 00 07 03 26 03 63 B0 )
[2015-06-27 23:19:27.555] [D] [zway] SENT ACK
[2015-06-27 23:19:27.556] [D] [zway] SETDATA devices.7.data.lastReceived = 0 (0x00000000)
[2015-06-27 23:19:27.558] [D] [zway] SETDATA devices.7.instances.0.commandClasses.38.data.level = 99 (0x00000063)
[2015-06-27 23:19:27.620] [D] [zway] RECEIVED: ( 01 09 00 04 00 07 03 26 03 63 B0 )
[2015-06-27 23:19:27.621] [D] [zway] SENT ACK
[2015-06-27 23:19:27.622] [D] [zway] SETDATA devices.7.data.lastReceived = 0 (0x00000000)
[2015-06-27 23:19:27.623] [D] [zway] SETDATA devices.7.instances.0.commandClasses.38.data.level = 99 (0x00000063)
[2015-06-27 23:19:27.702] [D] [zway] RECEIVED: ( 01 09 00 04 00 07 03 26 03 63 B0 )
[2015-06-27 23:19:27.703] [D] [zway] SENT ACK
[2015-06-27 23:19:27.703] [D] [zway] SETDATA devices.7.data.lastReceived = 0 (0x00000000)
[2015-06-27 23:19:27.703] [D] [zway] SETDATA devices.7.instances.0.commandClasses.38.data.level = 99 (0x00000063)
[2015-06-27 23:19:31.033] [I] [zway] Adding job: SwitchMultilevel Get
[2015-06-27 23:19:33.588] [D] [zway] RECEIVED: ( 01 05 00 13 07 00 EE )
[2015-06-27 23:19:33.589] [D] [zway] SENT ACK
[2015-06-27 23:19:33.590] [I] [zway] Job 0x13 (MultiChannel Version Get): Delivered
[2015-06-27 23:19:33.592] [D] [zway] SETDATA devices.11.data.lastPacketInfo.delivered = True
[2015-06-27 23:19:33.593] [D] [zway] SETDATA devices.11.data.lastPacketInfo.packetLength = 6 (0x00000006)
[2015-06-27 23:19:33.594] [D] [zway] SETDATA devices.11.data.lastPacketInfo.deliveryTime = 6050 (0x000017a2)
[2015-06-27 23:19:33.595] [D] [zway] SETDATA devices.11.data.lastPacketInfo = **********
[2015-06-27 23:19:33.596] [D] [zway] SendData Response with callback 0x07 received: received by recipient
[2015-06-27 23:19:33.597] [D] [zway] SETDATA devices.11.data.lastSend = 25333697 (0x01828fc1)
[2015-06-27 23:19:33.599] [D] [zway] Job 0x13 (MultiChannel Version Get): success
[2015-06-27 23:19:33.600] [I] [zway] Removing job: MultiChannel Version Get
[2015-06-27 23:19:33.601] [D] [zway] SENDING (cb 0x08): ( 01 09 00 13 07 02 26 02 25 08 E9 )
[2015-06-27 23:19:33.604] [D] [zway] RECEIVED ACK
[2015-06-27 23:19:33.606] [D] [zway] RECEIVED: ( 01 04 01 13 01 E8 )
[2015-06-27 23:19:33.607] [D] [zway] SENT ACK
[2015-06-27 23:19:33.608] [D] [zway] Delivered to Z-Wave stack
[2015-06-27 23:19:33.635] [D] [zway] RECEIVED: ( 01 0A 00 04 00 0B 04 86 14 60 03 0F )
[2015-06-27 23:19:33.636] [D] [zway] SENT ACK
[2015-06-27 23:19:33.636] [D] [zway] SETDATA devices.11.data.lastReceived = 0 (0x00000000)
[2015-06-27 23:19:33.638] [I] [zway] Node 11:0 CC Version: MultiChannel is v3
[2015-06-27 23:19:33.639] [D] [zway] SETDATA devices.11.instances.0.commandClasses.96.data.version = 3 (0x00000003)
[2015-06-27 23:19:33.767] [D] [zway] RECEIVED: ( 01 0A 00 04 00 0B 04 86 14 60 03 0F )
[2015-06-27 23:19:33.768] [D] [zway] SENT ACK
[2015-06-27 23:19:33.768] [D] [zway] SETDATA devices.11.data.lastReceived = 0 (0x00000000)
[2015-06-27 23:19:33.770] [I] [zway] Node 11:0 CC Version: MultiChannel is v3
[2015-06-27 23:19:33.771] [D] [zway] SETDATA devices.11.instances.0.commandClasses.96.data.version = 3 (0x00000003)
[2015-06-27 23:19:33.852] [D] [zway] RECEIVED: ( 01 05 00 13 08 00 E1 )
[2015-06-27 23:19:33.853] [D] [zway] SENT ACK
[2015-06-27 23:19:33.855] [I] [zway] Job 0x13 (SwitchMultilevel Get): Delivered
[2015-06-27 23:19:33.856] [D] [zway] SETDATA devices.7.data.lastPacketInfo.delivered = True
[2015-06-27 23:19:33.857] [D] [zway] SETDATA devices.7.data.lastPacketInfo.packetLength = 5 (0x00000005)
[2015-06-27 23:19:33.859] [D] [zway] SETDATA devices.7.data.lastPacketInfo.deliveryTime = 247 (0x000000f7)
[2015-06-27 23:19:33.860] [D] [zway] SETDATA devices.7.data.lastPacketInfo = **********
[2015-06-27 23:19:33.861] [D] [zway] SendData Response with callback 0x08 received: received by recipient
[2015-06-27 23:19:33.862] [D] [zway] SETDATA devices.7.data.lastSend = 25333723 (0x01828fdb)
[2015-06-27 23:19:33.863] [D] [zway] Job 0x13 (SwitchMultilevel Get): success
[2015-06-27 23:19:33.864] [I] [zway] Removing job: SwitchMultilevel Get
[2015-06-27 23:19:33.865] [D] [zway] SENDING (cb 0x09): ( 01 0A 00 13 0B 03 86 13 70 05 09 07 )
[2015-06-27 23:19:33.868] [D] [zway] RECEIVED ACK
[2015-06-27 23:19:33.871] [D] [zway] RECEIVED: ( 01 04 01 13 01 E8 )
[2015-06-27 23:19:33.871] [D] [zway] SENT ACK
[2015-06-27 23:19:33.872] [D] [zway] Delivered to Z-Wave stack
[2015-06-27 23:19:33.896] [D] [zway] RECEIVED: ( 01 09 00 04 00 07 03 26 03 63 B0 )
[2015-06-27 23:19:33.897] [D] [zway] SENT ACK
[2015-06-27 23:19:33.898] [D] [zway] SETDATA devices.7.data.lastReceived = 0 (0x00000000)
[2015-06-27 23:19:33.899] [D] [zway] SETDATA devices.7.instances.0.commandClasses.38.data.level = 99 (0x00000063)
[2015-06-27 23:19:33.957] [D] [zway] RECEIVED: ( 01 09 00 04 00 07 03 26 03 63 B0 )
[2015-06-27 23:19:33.958] [D] [zway] SENT ACK
[2015-06-27 23:19:33.959] [D] [zway] SETDATA devices.7.data.lastReceived = 0 (0x00000000)
[2015-06-27 23:19:33.961] [D] [zway] SETDATA devices.7.instances.0.commandClasses.38.data.level = 99 (0x00000063)
[2015-06-27 23:19:33.987] [D] [zway] RECEIVED: ( 01 09 00 04 00 07 03 26 03 63 B0 )
[2015-06-27 23:19:33.988] [D] [zway] SENT ACK
[2015-06-27 23:19:33.989] [D] [zway] SETDATA devices.7.data.lastReceived = 0 (0x00000000)
[2015-06-27 23:19:33.990] [D] [zway] SETDATA devices.7.instances.0.commandClasses.38.data.level = 99 (0x00000063)
[2015-06-27 23:19:37.000] [D] [zway] Job 0x13: deleted from queue
[2015-06-27 23:19:37.358] [I] [zway] Adding job: SwitchMultilevel Get
[2015-06-27 23:19:38.257] [D] [zway] Job 0x13: deleted from queue
[2015-06-27 23:19:39.631] [D] [zway] Job 0x13: deleted from queue
[2015-06-27 23:19:39.931] [D] [zway] RECEIVED: ( 01 05 00 13 09 00 E0 )
[2015-06-27 23:19:39.933] [D] [zway] SENT ACK
[2015-06-27 23:19:39.933] [I] [zway] Job 0x13 (Configuration Version Get): Delivered
[2015-06-27 23:19:39.934] [D] [zway] SETDATA devices.11.data.lastPacketInfo.delivered = True
[2015-06-27 23:19:39.936] [D] [zway] SETDATA devices.11.data.lastPacketInfo.packetLength = 6 (0x00000006)
[2015-06-27 23:19:39.937] [D] [zway] SETDATA devices.11.data.lastPacketInfo.deliveryTime = 6060 (0x000017ac)
[2015-06-27 23:19:39.938] [D] [zway] SETDATA devices.11.data.lastPacketInfo = **********
[2015-06-27 23:19:39.939] [D] [zway] SendData Response with callback 0x09 received: received by recipient
[2015-06-27 23:19:39.940] [D] [zway] SETDATA devices.11.data.lastSend = 25334315 (0x0182922b)
[2015-06-27 23:19:39.941] [D] [zway] Job 0x13 (Configuration Version Get): success
[2015-06-27 23:19:39.942] [I] [zway] Removing job: Configuration Version Get
[2015-06-27 23:19:39.944] [D] [zway] SENDING (cb 0x0a): ( 01 09 00 13 07 02 26 02 25 0A EB )
[2015-06-27 23:19:39.946] [D] [zway] RECEIVED ACK
[2015-06-27 23:19:39.949] [D] [zway] RECEIVED: ( 01 04 01 13 01 E8 )
[2015-06-27 23:19:39.950] [D] [zway] SENT ACK
[2015-06-27 23:19:39.951] [D] [zway] Delivered to Z-Wave stack
[2015-06-27 23:19:39.975] [D] [zway] RECEIVED: ( 01 0A 00 04 00 0B 04 86 14 70 01 1D )
[2015-06-27 23:19:39.976] [D] [zway] SENT ACK
[2015-06-27 23:19:39.977] [D] [zway] SETDATA devices.11.data.lastReceived = 0 (0x00000000)
[2015-06-27 23:19:39.978] [I] [zway] Node 11:0 CC Version: Configuration is v1
[2015-06-27 23:19:39.979] [D] [zway] SETDATA devices.11.instances.0.commandClasses.112.data.version = 1 (0x00000001)
[2015-06-27 23:19:40.107] [D] [zway] RECEIVED: ( 01 0A 00 04 00 0B 04 86 14 70 01 1D )
[2015-06-27 23:19:40.108] [D] [zway] SENT ACK
[2015-06-27 23:19:40.109] [D] [zway] SETDATA devices.11.data.lastReceived = 0 (0x00000000)
[2015-06-27 23:19:40.110] [I] [zway] Node 11:0 CC Version: Configuration is v1
[2015-06-27 23:19:40.112] [D] [zway] SETDATA devices.11.instances.0.commandClasses.112.data.version = 1 (0x00000001)
[2015-06-27 23:19:40.169] [D] [zway] RECEIVED: ( 01 0A 00 04 00 0B 04 86 14 70 01 1D )
[2015-06-27 23:19:40.170] [D] [zway] SENT ACK
[2015-06-27 23:19:40.170] [D] [zway] SETDATA devices.11.data.lastReceived = 0 (0x00000000)
[2015-06-27 23:19:40.172] [I] [zway] Node 11:0 CC Version: Configuration is v1
[2015-06-27 23:19:40.173] [D] [zway] SETDATA devices.11.instances.0.commandClasses.112.data.version = 1 (0x00000001)
[2015-06-27 23:19:40.265] [D] [zway] RECEIVED: ( 01 05 00 13 0A 00 E3 )
[2015-06-27 23:19:40.266] [D] [zway] SENT ACK
[2015-06-27 23:19:40.267] [I] [zway] Job 0x13 (SwitchMultilevel Get): Delivered
[2015-06-27 23:19:40.268] [D] [zway] SETDATA devices.7.data.lastPacketInfo.delivered = True
[2015-06-27 23:19:40.269] [D] [zway] SETDATA devices.7.data.lastPacketInfo.packetLength = 5 (0x00000005)
[2015-06-27 23:19:40.270] [D] [zway] SETDATA devices.7.data.lastPacketInfo.deliveryTime = 316 (0x0000013c)
[2015-06-27 23:19:40.272] [D] [zway] SETDATA devices.7.data.lastPacketInfo = **********
[2015-06-27 23:19:40.273] [D] [zway] SendData Response with callback 0x0a received: received by recipient
[2015-06-27 23:19:40.274] [D] [zway] SETDATA devices.7.data.lastSend = 25334347 (0x0182924b)
[2015-06-27 23:19:40.275] [D] [zway] Job 0x13 (SwitchMultilevel Get): success
[2015-06-27 23:19:40.276] [I] [zway] Removing job: SwitchMultilevel Get
[2015-06-27 23:19:40.279] [D] [zway] SENDING (cb 0x0b): ( 01 0A 00 13 0B 03 86 13 72 05 0B 07 )
[2015-06-27 23:19:40.281] [D] [zway] RECEIVED ACK
[2015-06-27 23:19:40.284] [D] [zway] RECEIVED: ( 01 04 01 13 01 E8 )
[2015-06-27 23:19:40.284] [D] [zway] SENT ACK
[2015-06-27 23:19:40.285] [D] [zway] Delivered to Z-Wave stack
[2015-06-27 23:19:40.309] [D] [zway] RECEIVED: ( 01 09 00 04 00 07 03 26 03 63 B0 )
[2015-06-27 23:19:40.310] [D] [zway] SENT ACK
[2015-06-27 23:19:40.311] [D] [zway] SETDATA devices.7.data.lastReceived = 0 (0x00000000)
[2015-06-27 23:19:40.312] [D] [zway] SETDATA devices.7.instances.0.commandClasses.38.data.level = 99 (0x00000063)
[2015-06-27 23:19:40.349] [D] [zway] RECEIVED: ( 01 09 00 04 00 07 03 26 03 63 B0 )
[2015-06-27 23:19:40.350] [D] [zway] SENT ACK
[2015-06-27 23:19:40.351] [D] [zway] SETDATA devices.7.data.lastReceived = 0 (0x00000000)
[2015-06-27 23:19:40.352] [D] [zway] SETDATA devices.7.instances.0.commandClasses.38.data.level = 99 (0x00000063)
[2015-06-27 23:19:40.420] [D] [zway] RECEIVED: ( 01 09 00 04 00 07 03 26 03 63 B0 )
[2015-06-27 23:19:40.421] [D] [zway] SENT ACK
[2015-06-27 23:19:40.422] [D] [zway] SETDATA devices.7.data.lastReceived = 0 (0x00000000)
[2015-06-27 23:19:40.423] [D] [zway] SETDATA devices.7.instances.0.commandClasses.38.data.level = 99 (0x00000063)
[2015-06-27 23:19:41.433] [D] [zway] Job 0x13: deleted from queue
[2015-06-27 23:19:41.464] [D] [zway] Job 0x13: deleted from queue
[2015-06-27 23:19:41.516] [D] [zway] Job 0x13: deleted from queue
[2015-06-27 23:19:44.298] [I] [zway] Adding job: SwitchMultilevel Get
[2015-06-27 23:19:46.344] [D] [zway] RECEIVED: ( 01 05 00 13 0B 00 E2 )
[2015-06-27 23:19:46.345] [D] [zway] SENT ACK
[2015-06-27 23:19:46.346] [I] [zway] Job 0x13 (ManufacturerSpecific Version Get): Delivered
[2015-06-27 23:19:46.348] [D] [zway] SETDATA devices.11.data.lastPacketInfo.delivered = True
[2015-06-27 23:19:46.349] [D] [zway] SETDATA devices.11.data.lastPacketInfo.packetLength = 6 (0x00000006)
[2015-06-27 23:19:46.350] [D] [zway] SETDATA devices.11.data.lastPacketInfo.deliveryTime = 6061 (0x000017ad)
[2015-06-27 23:19:46.351] [D] [zway] SETDATA devices.11.data.lastPacketInfo = **********
[2015-06-27 23:19:46.352] [D] [zway] SendData Response with callback 0x0b received: received by recipient
[2015-06-27 23:19:46.353] [D] [zway] SETDATA devices.11.data.lastSend = 25334916 (0x01829484)
[2015-06-27 23:19:46.354] [D] [zway] Job 0x13 (ManufacturerSpecific Version Get): success
[2015-06-27 23:19:46.356] [I] [zway] Removing job: ManufacturerSpecific Version Get
[2015-06-27 23:19:46.358] [D] [zway] SENDING (cb 0x0c): ( 01 09 00 13 07 02 26 02 25 0C ED )
[2015-06-27 23:19:46.360] [D] [zway] RECEIVED ACK
[2015-06-27 23:19:46.363] [D] [zway] RECEIVED: ( 01 04 01 13 01 E8 )
[2015-06-27 23:19:46.364] [D] [zway] SENT ACK
[2015-06-27 23:19:46.364] [D] [zway] Delivered to Z-Wave stack
[2015-06-27 23:19:46.390] [D] [zway] RECEIVED: ( 01 0A 00 04 00 0B 04 86 14 72 01 1F )
[2015-06-27 23:19:46.391] [D] [zway] SENT ACK
[2015-06-27 23:19:46.391] [D] [zway] SETDATA devices.11.data.lastReceived = 0 (0x00000000)
[2015-06-27 23:19:46.392] [I] [zway] Node 11:0 CC Version: ManufacturerSpecific is v1
[2015-06-27 23:19:46.393] [D] [zway] SETDATA devices.11.instances.0.commandClasses.114.data.version = 1 (0x00000001)
[2015-06-27 23:19:46.544] [D] [zway] RECEIVED: ( 01 0A 00 04 00 0B 04 86 14 72 01 1F )
[2015-06-27 23:19:46.544] [D] [zway] SENT ACK
[2015-06-27 23:19:46.544] [D] [zway] SETDATA devices.11.data.lastReceived = 0 (0x00000000)
[2015-06-27 23:19:46.545] [I] [zway] Node 11:0 CC Version: ManufacturerSpecific is v1
[2015-06-27 23:19:46.545] [D] [zway] SETDATA devices.11.instances.0.commandClasses.114.data.version = 1 (0x00000001)
[2015-06-27 23:19:46.618] [D] [zway] RECEIVED: ( 01 05 00 13 0C 00 E5 )
[2015-06-27 23:19:46.618] [D] [zway] SENT ACK
[2015-06-27 23:19:46.618] [I] [zway] Job 0x13 (SwitchMultilevel Get): Delivered
[2015-06-27 23:19:46.618] [D] [zway] SETDATA devices.7.data.lastPacketInfo.delivered = True
[2015-06-27 23:19:46.618] [D] [zway] SETDATA devices.7.data.lastPacketInfo.packetLength = 5 (0x00000005)
[2015-06-27 23:19:46.619] [D] [zway] SETDATA devices.7.data.lastPacketInfo.deliveryTime = 252 (0x000000fc)
[2015-06-27 23:19:46.619] [D] [zway] SETDATA devices.7.data.lastPacketInfo = **********
[2015-06-27 23:19:46.619] [D] [zway] SendData Response with callback 0x0c received: received by recipient
[2015-06-27 23:19:46.619] [D] [zway] SETDATA devices.7.data.lastSend = 25334943 (0x0182949f)
[2015-06-27 23:19:46.619] [D] [zway] Job 0x13 (SwitchMultilevel Get): success
[2015-06-27 23:19:46.619] [I] [zway] Removing job: SwitchMultilevel Get
[2015-06-27 23:19:46.620] [D] [zway] SENDING (cb 0x0d): ( 01 0A 00 13 0B 03 86 13 80 05 0D F3 )
[2015-06-27 23:19:46.626] [D] [zway] RECEIVED ACK
[2015-06-27 23:19:46.627] [D] [zway] RECEIVED: ( 01 04 01 13 01 E8 )
[2015-06-27 23:19:46.628] [D] [zway] SENT ACK
[2015-06-27 23:19:46.629] [D] [zway] Delivered to Z-Wave stack
[2015-06-27 23:19:46.748] [D] [zway] RECEIVED: ( 01 09 00 04 00 07 03 26 03 63 B0 )
[2015-06-27 23:19:46.749] [D] [zway] SENT ACK
[2015-06-27 23:19:46.750] [D] [zway] SETDATA devices.7.data.lastReceived = 0 (0x00000000)
[2015-06-27 23:19:46.751] [D] [zway] SETDATA devices.7.instances.0.commandClasses.38.data.level = 99 (0x00000063)
[2015-06-27 23:19:46.835] [D] [zway] RECEIVED: ( 01 09 00 04 00 07 03 26 03 63 B0 )
[2015-06-27 23:19:46.837] [D] [zway] SENT ACK
[2015-06-27 23:19:46.839] [D] [zway] SETDATA devices.7.data.lastReceived = 0 (0x00000000)
[2015-06-27 23:19:46.840] [D] [zway] SETDATA devices.7.instances.0.commandClasses.38.data.level = 99 (0x00000063)
[2015-06-27 23:19:47.397] [D] [zway] RECEIVED: ( 01 09 00 04 10 07 03 26 03 63 A0 )
[2015-06-27 23:19:47.397] [D] [zway] SENT ACK
[2015-06-27 23:19:47.398] [D] [zway] SETDATA devices.7.data.lastReceived = 0 (0x00000000)
[2015-06-27 23:19:47.399] [D] [zway] SETDATA devices.7.instances.0.commandClasses.38.data.level = 99 (0x00000063)
[2015-06-27 23:19:47.759] [D] [zway] Job 0x13: deleted from queue
[2015-06-27 23:19:48.126] [D] [zway] Job 0x13: deleted from queue
[2015-06-27 23:19:49.749] [I] [zway] Adding job: SwitchMultilevel Get
[2015-06-27 23:19:50.750] [D] [zway] Job 0x13 (SwitchMultilevel Get): removing duplicate
[2015-06-27 23:19:52.744] [D] [zway] RECEIVED: ( 01 05 00 13 0D 00 E4 )
[2015-06-27 23:19:52.745] [D] [zway] SENT ACK
[2015-06-27 23:19:52.746] [I] [zway] Job 0x13 (Battery Version Get): Delivered
[2015-06-27 23:19:52.747] [D] [zway] SETDATA devices.11.data.lastPacketInfo.delivered = True
[2015-06-27 23:19:52.749] [D] [zway] SETDATA devices.11.data.lastPacketInfo.packetLength = 6 (0x00000006)
[2015-06-27 23:19:52.750] [D] [zway] SETDATA devices.11.data.lastPacketInfo.deliveryTime = 6117 (0x000017e5)
[2015-06-27 23:19:52.751] [D] [zway] SETDATA devices.11.data.lastPacketInfo = **********
[2015-06-27 23:19:52.753] [D] [zway] SendData Response with callback 0x0d received: received by recipient
[2015-06-27 23:19:52.754] [D] [zway] SETDATA devices.11.data.lastSend = 25335539 (0x018296f3)
[2015-06-27 23:19:52.755] [D] [zway] Job 0x13 (Battery Version Get): success
[2015-06-27 23:19:52.756] [I] [zway] Removing job: Battery Version Get
[2015-06-27 23:19:52.758] [D] [zway] SENDING (cb 0x0e): ( 01 09 00 13 07 02 26 02 25 0E EF )
[2015-06-27 23:19:52.761] [D] [zway] RECEIVED ACK
[2015-06-27 23:19:52.763] [D] [zway] RECEIVED: ( 01 04 01 13 01 E8 )
[2015-06-27 23:19:52.764] [D] [zway] SENT ACK
[2015-06-27 23:19:52.765] [D] [zway] Delivered to Z-Wave stack
[2015-06-27 23:19:52.810] [D] [zway] RECEIVED: ( 01 0A 00 04 00 0B 04 86 14 80 01 ED )
[2015-06-27 23:19:52.811] [D] [zway] SENT ACK
[2015-06-27 23:19:52.812] [D] [zway] SETDATA devices.11.data.lastReceived = 0 (0x00000000)
[2015-06-27 23:19:52.813] [I] [zway] Node 11:0 CC Version: Battery is v1
[2015-06-27 23:19:52.814] [D] [zway] SETDATA devices.11.instances.0.commandClasses.128.data.version = 1 (0x00000001)
[2015-06-27 23:19:52.851] [D] [zway] RECEIVED: ( 01 0A 00 04 00 0B 04 86 14 80 01 ED )
[2015-06-27 23:19:52.852] [D] [zway] SENT ACK
[2015-06-27 23:19:52.853] [D] [zway] SETDATA devices.11.data.lastReceived = 0 (0x00000000)
[2015-06-27 23:19:52.853] [I] [zway] Node 11:0 CC Version: Battery is v1
[2015-06-27 23:19:52.854] [D] [zway] SETDATA devices.11.instances.0.commandClasses.128.data.version = 1 (0x00000001)
[2015-06-27 23:19:52.961] [D] [zway] RECEIVED: ( 01 0A 00 04 00 0B 04 86 14 80 01 ED )
[2015-06-27 23:19:52.961] [D] [zway] SENT ACK
[2015-06-27 23:19:52.961] [D] [zway] SETDATA devices.11.data.lastReceived = 0 (0x00000000)
[2015-06-27 23:19:52.962] [I] [zway] Node 11:0 CC Version: Battery is v1
[2015-06-27 23:19:52.962] [D] [zway] SETDATA devices.11.instances.0.commandClasses.128.data.version = 1 (0x00000001)
[2015-06-27 23:19:53.078] [D] [zway] RECEIVED: ( 01 05 00 13 0E 00 E7 )
[2015-06-27 23:19:53.078] [D] [zway] SENT ACK
[2015-06-27 23:19:53.078] [I] [zway] Job 0x13 (SwitchMultilevel Get): Delivered
[2015-06-27 23:19:53.078] [D] [zway] SETDATA devices.7.data.lastPacketInfo.delivered = True
[2015-06-27 23:19:53.079] [D] [zway] SETDATA devices.7.data.lastPacketInfo.packetLength = 5 (0x00000005)
[2015-06-27 23:19:53.079] [D] [zway] SETDATA devices.7.data.lastPacketInfo.deliveryTime = 313 (0x00000139)
[2015-06-27 23:19:53.079] [D] [zway] SETDATA devices.7.data.lastPacketInfo = **********
[2015-06-27 23:19:53.079] [D] [zway] SendData Response with callback 0x0e received: received by recipient
[2015-06-27 23:19:53.079] [D] [zway] SETDATA devices.7.data.lastSend = 25335570 (0x01829712)
[2015-06-27 23:19:53.079] [D] [zway] Job 0x13 (SwitchMultilevel Get): success
[2015-06-27 23:19:53.079] [I] [zway] Removing job: SwitchMultilevel Get
[2015-06-27 23:19:53.080] [D] [zway] SENDING (cb 0x0f): ( 01 0A 00 13 0B 03 86 13 81 05 0F F0 )
[2015-06-27 23:19:53.083] [D] [zway] RECEIVED ACK
[2015-06-27 23:19:53.085] [D] [zway] RECEIVED: ( 01 04 01 13 01 E8 )
[2015-06-27 23:19:53.086] [D] [zway] SENT ACK
[2015-06-27 23:19:53.087] [D] [zway] Delivered to Z-Wave stack
[2015-06-27 23:19:53.115] [D] [zway] RECEIVED: ( 01 09 00 04 00 07 03 26 03 63 B0 )
[2015-06-27 23:19:53.115] [D] [zway] SENT ACK
[2015-06-27 23:19:53.115] [D] [zway] SETDATA devices.7.data.lastReceived = 0 (0x00000000)
[2015-06-27 23:19:53.115] [D] [zway] SETDATA devices.7.instances.0.commandClasses.38.data.level = 99 (0x00000063)
[2015-06-27 23:19:53.166] [D] [zway] RECEIVED: ( 01 09 00 04 00 07 03 26 03 63 B0 )
[2015-06-27 23:19:53.167] [D] [zway] SENT ACK
[2015-06-27 23:19:53.168] [D] [zway] SETDATA devices.7.data.lastReceived = 0 (0x00000000)
[2015-06-27 23:19:53.169] [D] [zway] SETDATA devices.7.instances.0.commandClasses.38.data.level = 99 (0x00000063)
[2015-06-27 23:19:53.248] [D] [zway] RECEIVED: ( 01 09 00 04 00 07 03 26 03 63 B0 )
[2015-06-27 23:19:53.249] [D] [zway] SENT ACK
[2015-06-27 23:19:53.249] [D] [zway] SETDATA devices.7.data.lastReceived = 0 (0x00000000)
[2015-06-27 23:19:53.251] [D] [zway] SETDATA devices.7.instances.0.commandClasses.38.data.level = 99 (0x00000063)
[2015-06-27 23:19:54.225] [D] [zway] Job 0x13: deleted from queue
[2015-06-27 23:19:54.450] [D] [zway] Job 0x13: deleted from queue
[2015-06-27 23:19:56.196] [I] [zway] Adding job: SwitchMultilevel Get
[2015-06-27 23:19:59.157] [D] [zway] RECEIVED: ( 01 05 00 13 0F 00 E6 )
[2015-06-27 23:19:59.158] [D] [zway] SENT ACK
[2015-06-27 23:19:59.159] [I] [zway] Job 0x13 (Clock Version Get): Delivered
[2015-06-27 23:19:59.160] [D] [zway] SETDATA devices.11.data.lastPacketInfo.delivered = True
[2015-06-27 23:19:59.162] [D] [zway] SETDATA devices.11.data.lastPacketInfo.packetLength = 6 (0x00000006)
[2015-06-27 23:19:59.163] [D] [zway] SETDATA devices.11.data.lastPacketInfo.deliveryTime = 6072 (0x000017b8)
[2015-06-27 23:19:59.164] [D] [zway] SETDATA devices.11.data.lastPacketInfo = **********
[2015-06-27 23:19:59.165] [D] [zway] SendData Response with callback 0x0f received: received by recipient
[2015-06-27 23:19:59.166] [D] [zway] SETDATA devices.11.data.lastSend = 25336160 (0x01829960)
[2015-06-27 23:19:59.167] [D] [zway] Job 0x13 (Clock Version Get): success
[2015-06-27 23:19:59.168] [I] [zway] Removing job: Clock Version Get
[2015-06-27 23:19:59.173] [D] [zway] SENDING (cb 0x10): ( 01 09 00 13 07 02 26 02 25 10 F1 )
[2015-06-27 23:19:59.175] [D] [zway] RECEIVED ACK
[2015-06-27 23:19:59.178] [D] [zway] RECEIVED: ( 01 04 01 13 01 E8 )
[2015-06-27 23:19:59.179] [D] [zway] SENT ACK
[2015-06-27 23:19:59.179] [D] [zway] Delivered to Z-Wave stack
[2015-06-27 23:19:59.214] [D] [zway] RECEIVED: ( 01 0A 00 04 00 0B 04 86 14 81 01 EC )
[2015-06-27 23:19:59.215] [D] [zway] SENT ACK
[2015-06-27 23:19:59.216] [D] [zway] SETDATA devices.11.data.lastReceived = 0 (0x00000000)
[2015-06-27 23:19:59.217] [I] [zway] Node 11:0 CC Version: Clock is v1
[2015-06-27 23:19:59.218] [D] [zway] SETDATA devices.11.instances.0.commandClasses.129.data.version = 1 (0x00000001)
[2015-06-27 23:19:59.317] [D] [zway] RECEIVED: ( 01 0A 00 04 00 0B 04 86 14 81 01 EC )
[2015-06-27 23:19:59.317] [D] [zway] SENT ACK
[2015-06-27 23:19:59.318] [D] [zway] SETDATA devices.11.data.lastReceived = 0 (0x00000000)
[2015-06-27 23:19:59.320] [I] [zway] Node 11:0 CC Version: Clock is v1
[2015-06-27 23:19:59.321] [D] [zway] SETDATA devices.11.instances.0.commandClasses.129.data.version = 1 (0x00000001)
[2015-06-27 23:19:59.411] [D] [zway] RECEIVED: ( 01 05 00 13 10 00 F9 )
[2015-06-27 23:19:59.412] [D] [zway] SENT ACK
[2015-06-27 23:19:59.413] [I] [zway] Job 0x13 (SwitchMultilevel Get): Delivered
[2015-06-27 23:19:59.414] [D] [zway] SETDATA devices.7.data.lastPacketInfo.delivered = True
[2015-06-27 23:19:59.415] [D] [zway] SETDATA devices.7.data.lastPacketInfo.packetLength = 5 (0x00000005)
[2015-06-27 23:19:59.416] [D] [zway] SETDATA devices.7.data.lastPacketInfo.deliveryTime = 233 (0x000000e9)
[2015-06-27 23:19:59.417] [D] [zway] SETDATA devices.7.data.lastPacketInfo = **********
[2015-06-27 23:19:59.419] [D] [zway] SendData Response with callback 0x10 received: received by recipient
[2015-06-27 23:19:59.420] [D] [zway] SETDATA devices.7.data.lastSend = 25336185 (0x01829979)
[2015-06-27 23:19:59.421] [D] [zway] Job 0x13 (SwitchMultilevel Get): success
[2015-06-27 23:19:59.422] [I] [zway] Removing job: SwitchMultilevel Get
[2015-06-27 23:19:59.423] [D] [zway] SENDING (cb 0x11): ( 01 0A 00 13 0B 03 86 13 85 05 11 EA )
[2015-06-27 23:19:59.426] [D] [zway] RECEIVED ACK
[2015-06-27 23:19:59.428] [D] [zway] RECEIVED: ( 01 04 01 13 01 E8 )
[2015-06-27 23:19:59.432] [D] [zway] SENT ACK
[2015-06-27 23:19:59.434] [D] [zway] Delivered to Z-Wave stack
[2015-06-27 23:19:59.502] [D] [zway] RECEIVED: ( 01 09 00 04 00 07 03 26 03 63 B0 )
[2015-06-27 23:19:59.503] [D] [zway] SENT ACK
[2015-06-27 23:19:59.503] [D] [zway] SETDATA devices.7.data.lastReceived = 0 (0x00000000)
[2015-06-27 23:19:59.503] [D] [zway] SETDATA devices.7.instances.0.commandClasses.38.data.level = 99 (0x00000063)
[2015-06-27 23:19:59.547] [D] [zway] RECEIVED: ( 01 09 00 04 00 07 03 26 03 63 B0 )
[2015-06-27 23:19:59.547] [D] [zway] SENT ACK
[2015-06-27 23:19:59.548] [D] [zway] SETDATA devices.7.data.lastReceived = 0 (0x00000000)
[2015-06-27 23:19:59.550] [D] [zway] SETDATA devices.7.instances.0.commandClasses.38.data.level = 99 (0x00000063)
[2015-06-27 23:20:00.538] [D] [zway] Job 0x13: deleted from queue
[2015-06-27 23:20:00.829] [D] [zway] RECEIVED: ( 01 05 00 13 11 00 F8 )
[2015-06-27 23:20:00.830] [D] [zway] SENT ACK
[2015-06-27 23:20:00.831] [I] [zway] Job 0x13 (Association Version Get): Delivered
[2015-06-27 23:20:00.832] [D] [zway] SETDATA devices.11.data.lastPacketInfo.delivered = True
[2015-06-27 23:20:00.834] [D] [zway] SETDATA devices.11.data.lastPacketInfo.packetLength = 6 (0x00000006)
[2015-06-27 23:20:00.835] [D] [zway] SETDATA devices.11.data.lastPacketInfo.deliveryTime = 1396 (0x00000574)
[2015-06-27 23:20:00.836] [D] [zway] SETDATA devices.11.data.lastPacketInfo = **********
[2015-06-27 23:20:00.837] [D] [zway] SendData Response with callback 0x11 received: received by recipient
[2015-06-27 23:20:00.838] [D] [zway] SETDATA devices.11.data.lastSend = 25336321 (0x01829a01)
[2015-06-27 23:20:00.839] [D] [zway] Job 0x13 (Association Version Get): success
[2015-06-27 23:20:00.840] [I] [zway] Removing job: Association Version Get
[2015-06-27 23:20:00.843] [D] [zway] Job 0x13: deleted from queue
[2015-06-27 23:20:00.906] [D] [zway] SENDING (cb 0x12): ( 01 0A 00 13 0B 03 86 13 86 05 12 EA )
[2015-06-27 23:20:00.908] [D] [zway] RECEIVED ACK
[2015-06-27 23:20:00.911] [D] [zway] RECEIVED: ( 01 04 01 13 01 E8 )
[2015-06-27 23:20:00.913] [D] [zway] SENT ACK
[2015-06-27 23:20:00.914] [D] [zway] Delivered to Z-Wave stack
[2015-06-27 23:20:00.938] [D] [zway] RECEIVED: ( 01 0A 00 04 00 0B 04 86 14 85 01 E8 )
[2015-06-27 23:20:00.939] [D] [zway] SENT ACK
[2015-06-27 23:20:00.940] [D] [zway] SETDATA devices.11.data.lastReceived = 0 (0x00000000)
[2015-06-27 23:20:00.941] [I] [zway] Node 11:0 CC Version: Association is v1
[2015-06-27 23:20:00.942] [D] [zway] SETDATA devices.11.instances.0.commandClasses.133.data.version = 1 (0x00000001)
[2015-06-27 23:20:00.943] [D] [zway] SETDATA devices.11.instances.1.commandClasses.133.data.version = 1 (0x00000001)
[2015-06-27 23:20:00.944] [D] [zway] SETDATA devices.11.instances.2.commandClasses.133.data.version = 1 (0x00000001)
[2015-06-27 23:20:01.029] [D] [zway] RECEIVED: ( 01 0A 00 04 00 0B 04 86 14 85 01 E8 )
[2015-06-27 23:20:01.030] [D] [zway] SENT ACK
[2015-06-27 23:20:01.031] [D] [zway] SETDATA devices.11.data.lastReceived = 0 (0x00000000)
[2015-06-27 23:20:01.032] [I] [zway] Node 11:0 CC Version: Association is v1
[2015-06-27 23:20:01.033] [D] [zway] SETDATA devices.11.instances.0.commandClasses.133.data.version = 1