New Eurotronic Radiator Thermostat
Any one who has seen this one? Hope it has upgradeable firmware, since there are too many flawed Z-Wave devices around
v2.1.1 raspi2
Re: New Eurotronic Radiator Thermostat
yes, we have tested. Mixed "feelings" ...
Seems not to be very stable - one of them canceled reporting after some hours - wthout any Z-Wave message.
deep deep sleep..... Must be woken up using micro switch.
SetPoint can be set - but manual setpoint setting at device will not be reported to gateway ! - this is important...
The manual setpoint will overwrite the Gateway setpoint for 2 hours - without notification.
The valve value will not be reported in standard mode (in manual is written, that can be read)
And - not sure about Z-Wave certification. Not listed at Z-Wave, not at Perpper1 - and no Z-Wave logo at the device/manual/box.
Eurotronics support did not answer to our questions in this time...
So... not sure in this time... a good one or not.
Last 3 days (after multiple tests and reset/reinclude) two devices are working stable....
Michael
Michael
Note that this TRV is fully based on Z-Wave part of previous Stella Z model. So, they share same firmwares. This means no need for certification (still same Z-Wave functionality). On the other side, this is a problem, since old one had no Association group to do unsolicited reports. With a wheel allowing to change locally this is now a problem.
Hmmm, awkward situation. Reading specifications never was easy for curstomers, but this one was not something I would expect as a customer.
May I assume the wheel setting can be overruled by the next Z-Wave temperature setting?
Yes, written in manual that it is working, and just tested again, value will be overwritten if you change the value in Z-Way.pz1 wrote:May I assume the wheel setting can be overruled by the next Z-Wave temperature setting?
Michael
today again.... strange issue.
Configuration: Z-Way rc17 / Razberry + Eurotronic, nothing else.
Was reporting fine all the time, then (full z-way log):
No values more between 10:10 and 11:01, and after 11:16 ....
before - and after (now is 12:10) (show only values here):
So ... summary... not stable.
Drops here in reporting, or in communication....
BTW - for testing the distance between Razberry and Thermostat is 3 meters only....
Michael
[2015-11-30 10:00:00.380] [I] [core] --- ZWayVDev_zway_2-0-49-1 performCommand processing: {"0":"update"}
[2015-11-30 10:00:00.381] [D] [zway] Job 0x13 (SensorMultilevel V1-4 Get): removing duplicate
[2015-11-30 10:02:00.793] [I] [core] --- ZWayVDev_zway_2-0-49-1 performCommand processing: {"0":"update"}
[2015-11-30 10:02:00.794] [D] [zway] Job 0x13 (SensorMultilevel V1-4 Get): removing duplicate
[2015-11-30 10:04:00.198] [I] [core] --- ZWayVDev_zway_2-0-49-1 performCommand processing: {"0":"update"}
[2015-11-30 10:04:00.198] [D] [zway] Job 0x13 (SensorMultilevel V1-4 Get): removing duplicate
[2015-11-30 10:06:00.594] [I] [core] --- ZWayVDev_zway_2-0-49-1 performCommand processing: {"0":"update"}
[2015-11-30 10:06:00.594] [D] [zway] Job 0x13 (SensorMultilevel V1-4 Get): removing duplicate
[2015-11-30 10:08:00.013] [I] [core] --- ZWayVDev_zway_2-0-49-1 performCommand processing: {"0":"update"}
[2015-11-30 10:08:00.013] [D] [zway] Job 0x13 (SensorMultilevel V1-4 Get): removing duplicate
[2015-11-30 10:10:00.414] [I] [core] --- ZWayVDev_zway_2-0-49-1 performCommand processing: {"0":"update"}
[2015-11-30 10:10:00.414] [D] [zway] Job 0x13 (SensorMultilevel V1-4 Get): removing duplicate
[2015-11-30 10:10:08.164] [D] [zway] RECEIVED: ( 01 08 00 04 00 02 02 84 07 70 )
[2015-11-30 10:10:08.164] [D] [zway] SENT ACK
[2015-11-30 10:10:08.164] [D] [zway] SETDATA devices.2.data.lastReceived = 0 (0x00000000)
[2015-11-30 10:10:08.164] [I] [zway] Node 2:0 CC Wakeup: Wakeup notification
[2015-11-30 10:10:08.164] [D] [zway] SETDATA devices.2.instances.0.commandClasses.132.data.lastWakeup = 1448874608 (0x565c1270)
[2015-11-30 10:10:08.165] [D] [zway] SETDATA devices.2.data.isAwake = True
[2015-11-30 10:10:08.165] [D] [zway] SETDATA devices.2.data.lastSend = 24015691 (0x016e734b)
[2015-11-30 10:10:08.165] [D] [zway] SETDATA devices.2.data.lastNonceGet = 24014691 (0x016e6f63)
[2015-11-30 10:10:08.165] [D] [zway] Running wakeup handler for node 2
[2015-11-30 10:10:08.165] [D] [zway] SETDATA devices.2.instances.0.commandClasses.132.data.lastSleep = 1448874608 (0x565c1270)
[2015-11-30 10:10:08.165] [I] [zway] Node 2:0 CC Wakeup: Send node to sleep
[2015-11-30 10:10:08.165] [I] [zway] Adding job: Wakeup Sleep
[2015-11-30 10:10:08.235] [D] [zway] SENDING (cb 0x41): ( 01 09 00 13 02 02 31 04 05 41 94 )
[2015-11-30 10:10:08.237] [D] [zway] RECEIVED ACK
[2015-11-30 10:10:08.240] [D] [zway] RECEIVED: ( 01 04 01 13 01 E8 )
[2015-11-30 10:10:08.240] [D] [zway] SENT ACK
[2015-11-30 10:10:08.240] [D] [zway] Delivered to Z-Wave stack
[2015-11-30 10:10:08.533] [D] [zway] RECEIVED: ( 01 05 00 13 41 01 A9 )
[2015-11-30 10:10:08.533] [D] [zway] SENT ACK
[2015-11-30 10:10:08.533] [I] [zway] Job 0x13 (SensorMultilevel V1-4 Get): Not delivered to recipient
[2015-11-30 10:10:08.534] [D] [zway] SETDATA devices.2.data.lastPacketInfo.delivered = False
[2015-11-30 10:10:08.534] [D] [zway] SETDATA devices.2.data.lastPacketInfo.packetLength = 5 (0x00000005)
[2015-11-30 10:10:08.534] [D] [zway] SETDATA devices.2.data.lastPacketInfo.deliveryTime = 293 (0x00000125)
[2015-11-30 10:10:08.534] [D] [zway] SETDATA devices.2.data.lastPacketInfo = **********
[2015-11-30 10:10:08.534] [D] [zway] SETDATA devices.2.data.isAwake = False
[2015-11-30 10:10:08.534] [D] [zway] Sending the queue for node 2 into sleep
[2015-11-30 10:10:12.451] [D] [zway] RECEIVED: ( 01 0C 00 04 00 02 06 31 05 01 22 00 8C 68 )
[2015-11-30 10:10:12.451] [D] [zway] SENT ACK
[2015-11-30 10:10:12.451] [D] [zway] SETDATA devices.2.data.lastReceived = 0 (0x00000000)
[2015-11-30 10:10:12.451] [D] [zway] SETDATA devices.2.instances.0.commandClasses.49.data.1.deviceScale = 0 (0x00000000)
[2015-11-30 10:10:12.453] [D] [zway] SETDATA devices.2.instances.0.commandClasses.49.data.1.scaleString = "°C"
[2015-11-30 10:10:12.453] [D] [zway] SETDATA devices.2.instances.0.commandClasses.49.data.1.val = 14.000000
[2015-11-30 10:10:12.453] [D] [zway] SETDATA devices.2.instances.0.commandClasses.49.data.1 = Empty
[2015-11-30 10:10:12.461] [D] [zway] RECEIVED: ( 01 0C 00 04 00 02 06 31 05 01 22 00 8C 68 )
[2015-11-30 10:10:12.462] [D] [zway] SENT ACK
[2015-11-30 10:10:12.462] [D] [zway] SETDATA devices.2.data.lastReceived = 0 (0x00000000)
[2015-11-30 10:10:12.462] [D] [zway] SETDATA devices.2.instances.0.commandClasses.49.data.1.deviceScale = 0 (0x00000000)
[2015-11-30 10:10:12.463] [D] [zway] SETDATA devices.2.instances.0.commandClasses.49.data.1.scaleString = "°C"
[2015-11-30 10:10:12.464] [D] [zway] SETDATA devices.2.instances.0.commandClasses.49.data.1.val = 14.000000
[2015-11-30 10:10:12.464] [D] [zway] SETDATA devices.2.instances.0.commandClasses.49.data.1 = Empty
[2015-11-30 10:10:12.481] [D] [zway] RECEIVED: ( 01 0C 00 04 00 02 06 31 05 01 22 00 8C 68 )
[2015-11-30 10:10:12.482] [D] [zway] SENT ACK
[2015-11-30 10:10:12.482] [D] [zway] SETDATA devices.2.data.lastReceived = 0 (0x00000000)
[2015-11-30 10:10:12.482] [D] [zway] SETDATA devices.2.instances.0.commandClasses.49.data.1.deviceScale = 0 (0x00000000)
[2015-11-30 10:10:12.483] [D] [zway] SETDATA devices.2.instances.0.commandClasses.49.data.1.scaleString = "°C"
[2015-11-30 10:10:12.483] [D] [zway] SETDATA devices.2.instances.0.commandClasses.49.data.1.val = 14.000000
[2015-11-30 10:10:12.484] [D] [zway] SETDATA devices.2.instances.0.commandClasses.49.data.1 = Empty
[2015-11-30 10:10:12.491] [D] [zway] RECEIVED: ( 01 0C 00 04 00 02 06 31 05 01 22 00 8C 68 )
[2015-11-30 10:10:12.491] [D] [zway] SENT ACK
[2015-11-30 10:10:12.491] [D] [zway] SETDATA devices.2.data.lastReceived = 0 (0x00000000)
[2015-11-30 10:10:12.491] [D] [zway] SETDATA devices.2.instances.0.commandClasses.49.data.1.deviceScale = 0 (0x00000000)
[2015-11-30 10:10:12.493] [D] [zway] SETDATA devices.2.instances.0.commandClasses.49.data.1.scaleString = "°C"
[2015-11-30 10:10:12.493] [D] [zway] SETDATA devices.2.instances.0.commandClasses.49.data.1.val = 14.000000
[2015-11-30 10:10:12.493] [D] [zway] SETDATA devices.2.instances.0.commandClasses.49.data.1 = Empty
[2015-11-30 10:10:12.502] [I] [core] Notification: device-info (device-temperature): {"dev":"Eurotronic Technology Temperature (2.0.49.1)","l":"14 °C"}
[2015-11-30 10:14:00.230] [I] [core] --- ZWayVDev_zway_2-0-49-1 performCommand processing: {"0":"update"}
[2015-11-30 10:14:00.230] [I] [zway] Job 0x13 (Wakeup Sleep): Cancelling job: Wakeup Sleep
[2015-11-30 10:14:00.230] [I] [zway] Removing job: Wakeup Sleep
[2015-11-30 10:14:00.230] [D] [zway] Job 0x13 (SensorMultilevel V1-4 Get): removing duplicate
[2015-11-30 10:14:20.375] [D] [zway] Job 0x13: deleted from queue
[2015-11-30 10:16:00.647] [I] [core] --- ZWayVDev_zway_2-0-49-1 performCommand processing: {"0":"update"}
[2015-11-30 10:16:00.648] [D] [zway] Job 0x13 (SensorMultilevel V1-4 Get): removing duplicate
[2015-11-30 10:18:00.080] [I] [core] --- ZWayVDev_zway_2-0-49-1 performCommand processing: {"0":"update"}
[2015-11-30 10:18:00.081] [D] [zway] Job 0x13 (SensorMultilevel V1-4 Get): removing duplicate
[2015-11-30 10:20:00.531] [I] [core] --- ZWayVDev_zway_2-0-49-1 performCommand processing: {"0":"update"}
[2015-11-30 10:20:00.531] [D] [zway] Job 0x13 (SensorMultilevel V1-4 Get): removing duplicate
[2015-11-30 10:22:00.937] [I] [core] --- ZWayVDev_zway_2-0-49-1 performCommand processing: {"0":"update"}
[2015-11-30 10:22:00.938] [D] [zway] Job 0x13 (SensorMultilevel V1-4 Get): removing duplicate
[2015-11-30 10:24:00.353] [I] [core] --- ZWayVDev_zway_2-0-49-1 performCommand processing: {"0":"update"}
[2015-11-30 10:24:00.354] [D] [zway] Job 0x13 (SensorMultilevel V1-4 Get): removing duplicate
[2015-11-30 10:26:00.773] [I] [core] --- ZWayVDev_zway_2-0-49-1 performCommand processing: {"0":"update"}
[2015-11-30 10:26:00.774] [D] [zway] Job 0x13 (SensorMultilevel V1-4 Get): removing duplicate
[2015-11-30 10:28:00.194] [I] [core] --- ZWayVDev_zway_2-0-49-1 performCommand processing: {"0":"update"}
[2015-11-30 10:28:00.195] [D] [zway] Job 0x13 (SensorMultilevel V1-4 Get): removing duplicate
[2015-11-30 10:30:00.604] [I] [core] --- ZWayVDev_zway_2-0-49-1 performCommand processing: {"0":"update"}
[2015-11-30 10:30:00.605] [D] [zway] Job 0x13 (SensorMultilevel V1-4 Get): removing duplicate
[2015-11-30 10:32:00.014] [I] [core] --- ZWayVDev_zway_2-0-49-1 performCommand processing: {"0":"update"}
[2015-11-30 10:32:00.014] [D] [zway] Job 0x13 (SensorMultilevel V1-4 Get): removing duplicate
[2015-11-30 10:34:00.446] [I] [core] --- ZWayVDev_zway_2-0-49-1 performCommand processing: {"0":"update"}
[2015-11-30 10:34:00.447] [D] [zway] Job 0x13 (SensorMultilevel V1-4 Get): removing duplicate
[2015-11-30 10:36:00.858] [I] [core] --- ZWayVDev_zway_2-0-49-1 performCommand processing: {"0":"update"}
[2015-11-30 10:36:00.858] [D] [zway] Job 0x13 (SensorMultilevel V1-4 Get): removing duplicate
[2015-11-30 10:38:00.265] [I] [core] --- ZWayVDev_zway_2-0-49-1 performCommand processing: {"0":"update"}
[2015-11-30 10:38:00.265] [D] [zway] Job 0x13 (SensorMultilevel V1-4 Get): removing duplicate
[2015-11-30 10:40:00.680] [I] [core] --- ZWayVDev_zway_2-0-49-1 performCommand processing: {"0":"update"}
[2015-11-30 10:40:00.681] [D] [zway] Job 0x13 (SensorMultilevel V1-4 Get): removing duplicate
[2015-11-30 10:42:00.082] [I] [core] --- ZWayVDev_zway_2-0-49-1 performCommand processing: {"0":"update"}
[2015-11-30 10:42:00.082] [D] [zway] Job 0x13 (SensorMultilevel V1-4 Get): removing duplicate
[2015-11-30 10:44:00.501] [I] [core] --- ZWayVDev_zway_2-0-49-1 performCommand processing: {"0":"update"}
[2015-11-30 10:44:00.502] [D] [zway] Job 0x13 (SensorMultilevel V1-4 Get): removing duplicate
[2015-11-30 10:46:00.932] [I] [core] --- ZWayVDev_zway_2-0-49-1 performCommand processing: {"0":"update"}
[2015-11-30 10:46:00.933] [D] [zway] Job 0x13 (SensorMultilevel V1-4 Get): removing duplicate
[2015-11-30 10:48:00.349] [I] [core] --- ZWayVDev_zway_2-0-49-1 performCommand processing: {"0":"update"}
[2015-11-30 10:48:00.350] [D] [zway] Job 0x13 (SensorMultilevel V1-4 Get): removing duplicate
[2015-11-30 10:50:00.763] [I] [core] --- ZWayVDev_zway_2-0-49-1 performCommand processing: {"0":"update"}
[2015-11-30 10:50:00.764] [D] [zway] Job 0x13 (SensorMultilevel V1-4 Get): removing duplicate
[2015-11-30 10:52:00.176] [I] [core] --- ZWayVDev_zway_2-0-49-1 performCommand processing: {"0":"update"}
[2015-11-30 10:52:00.177] [D] [zway] Job 0x13 (SensorMultilevel V1-4 Get): removing duplicate
[2015-11-30 10:54:00.601] [I] [core] --- ZWayVDev_zway_2-0-49-1 performCommand processing: {"0":"update"}
[2015-11-30 10:54:00.601] [D] [zway] Job 0x13 (SensorMultilevel V1-4 Get): removing duplicate
[2015-11-30 10:56:00.004] [I] [core] --- ZWayVDev_zway_2-0-49-1 performCommand processing: {"0":"update"}
[2015-11-30 10:56:00.005] [D] [zway] Job 0x13 (SensorMultilevel V1-4 Get): removing duplicate
[2015-11-30 10:58:00.445] [I] [core] --- ZWayVDev_zway_2-0-49-1 performCommand processing: {"0":"update"}
[2015-11-30 10:58:00.446] [D] [zway] Job 0x13 (SensorMultilevel V1-4 Get): removing duplicate
[2015-11-30 07:48:24.976] [D] [zway] SETDATA devices.2.instances.0.commandClasses.49.data.1.val = 18.500000
[2015-11-30 07:53:26.211] [D] [zway] SETDATA devices.2.instances.0.commandClasses.49.data.1.val = 18.000000
[2015-11-30 07:58:27.483] [D] [zway] SETDATA devices.2.instances.0.commandClasses.49.data.1.val = 17.000000
[2015-11-30 08:04:28.133] [D] [zway] SETDATA devices.2.instances.0.commandClasses.49.data.1.val = 16.500000
[2015-11-30 08:09:29.343] [D] [zway] SETDATA devices.2.instances.0.commandClasses.49.data.1.val = 16.000000
[2015-11-30 08:14:30.534] [D] [zway] SETDATA devices.2.instances.0.commandClasses.49.data.1.val = 15.500000
[2015-11-30 08:19:31.916] [D] [zway] SETDATA devices.2.instances.0.commandClasses.49.data.1.val = 15.500000
[2015-11-30 08:24:33.445] [D] [zway] SETDATA devices.2.instances.0.commandClasses.49.data.1.val = 14.500000
[2015-11-30 08:29:34.805] [D] [zway] SETDATA devices.2.instances.0.commandClasses.49.data.1.val = 14.500000
[2015-11-30 08:34:36.096] [D] [zway] SETDATA devices.2.instances.0.commandClasses.49.data.1.val = 14.000000
[2015-11-30 08:39:37.397] [D] [zway] SETDATA devices.2.instances.0.commandClasses.49.data.1.val = 12.500000
[2015-11-30 08:44:38.347] [D] [zway] SETDATA devices.2.instances.0.commandClasses.49.data.1.val = 12.000000
[2015-11-30 08:49:39.638] [D] [zway] SETDATA devices.2.instances.0.commandClasses.49.data.1.val = 11.000000
[2015-11-30 08:54:40.865] [D] [zway] SETDATA devices.2.instances.0.commandClasses.49.data.1.val = 11.000000
[2015-11-30 08:59:42.175] [D] [zway] SETDATA devices.2.instances.0.commandClasses.49.data.1.val = 11.000000
[2015-11-30 09:04:43.535] [D] [zway] SETDATA devices.2.instances.0.commandClasses.49.data.1.val = 10.500000
[2015-11-30 09:09:44.717] [D] [zway] SETDATA devices.2.instances.0.commandClasses.49.data.1.val = 11.000000
[2015-11-30 09:14:46.041] [D] [zway] SETDATA devices.2.instances.0.commandClasses.49.data.1.val = 11.000000
[2015-11-30 09:19:47.173] [D] [zway] SETDATA devices.2.instances.0.commandClasses.49.data.1.val = 11.000000
[2015-11-30 09:24:48.482] [D] [zway] SETDATA devices.2.instances.0.commandClasses.49.data.1.val = 11.000000
[2015-11-30 09:29:49.813] [D] [zway] SETDATA devices.2.instances.0.commandClasses.49.data.1.val = 11.000000
[2015-11-30 09:34:51.291] [D] [zway] SETDATA devices.2.instances.0.commandClasses.49.data.1.val = 11.000000
[2015-11-30 09:39:52.440] [D] [zway] SETDATA devices.2.instances.0.commandClasses.49.data.1.val = 11.500000
[2015-11-30 09:44:53.601] [D] [zway] SETDATA devices.2.instances.0.commandClasses.49.data.1.val = 11.500000
[2015-11-30 09:49:54.831] [D] [zway] SETDATA devices.2.instances.0.commandClasses.49.data.1.val = 11.500000
[2015-11-30 09:54:56.055] [D] [zway] SETDATA devices.2.instances.0.commandClasses.49.data.1.val = 11.500000
[2015-11-30 11:01:11.050] [D] [zway] SETDATA devices.2.instances.0.commandClasses.49.data.1.val = 17.500000
[2015-11-30 11:16:52.347] [D] [zway] SETDATA devices.2.instances.0.commandClasses.49.data.1.val = 18.000000
Michael
Have you filtered second log? If not, it can not be true - values can not change without a RECEIVED command unless you explicitelly use API to change that value.
no, I haven't filtered.
I already think that the Z-Wave chip have any problem.
Yesterday there was a big "nothing" ... today in the morning the thermostat began to send again....
Michael
Michael
Michael, changes of dataholders withou RECEIVED are possible only via API. So, it comes not from Z-Wave network